    Replace a 36 year old Line Set?

    I need to replace the split system AC in my 36 year old house. The line set is original to the house as far as I can tell. One tech told me he could just flush the lines and there was no need to replace them. Sounds like non-sense to me. What do you pros think?

  2. #2
    Join Date
    Dec 2007
    Location
    Ohio
    Posts
    2,876
    Quote Originally Posted by maddog82 View Post
    I need to replace the split system AC in my 36 year old house. The line set is original to the house as far as I can tell. One tech told me he could just flush the lines and there was no need to replace them. Sounds like non-sense to me. What do you pros think?
    If it is REALLY 36 years old.....its the wrong size for your new unit.....replace it!
    I need a new signature.....

  3. #3
    Join Date
    Jul 2009
    Location
    S.E.,PA
    Posts
    99
    I agree, for a little more cost it should be replaced especially if there are any joints in it. Either way replace it.
    Even a blind squirrel can find a nut every now and then.

  4. #4
    Join Date
    Sep 2004
    Location
    Fort Worth, Texas
    Posts
    586
    Replace the lineset. Replacing the lineset should be part of any new install. The guy that suggested flushing the lines is just being lazy. Being 36 years old the lineset is probably not the only thing that needs to be replaced.

    New Lineset
    New Thermostat & Wiring
    New Pad (for the unit to sit on)
    New drain piping
    Duct work (it is hard to say without looking at the system, but you could probably benefit from new duct work.
    New Electrical Disconnect & Wiring Whip

    You could get away without replacing all those things. However, if it were my house I would do these things. It will be cheaper to do these things as part of a changeout vs. having to come back and replace them ala carte later on.
    Last edited by rubberduck; 09-11-2009 at 10:30 PM. Reason: a
    Installs, Changeouts, & Heat Stroke.....not necessarily in that order

  5. #5
    Thanks guys. I'll cross him off the list. I'll replace the suggested items as well.

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,081
    Quote Originally Posted by I_bend_metal View Post
    If it is REALLY 36 years old.....its the wrong size for your new unit.....replace it!
    Thats not true. Lots of old line sets are still the correct size for new systems.

    While I prefer to change the line set. It is not actually required in many applications.


    OP: Do you know what size your line set is? If so, could you please post it. Along with the size of the new proposed unit.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,081
    Quote Originally Posted by maddog82 View Post
    Thanks guys. I'll cross him off the list. I'll replace the suggested items as well.
    He was not lying to you. Nor is he misinformed. Don't be too quick to cross him off the list.

    I'm not saying you should use him. But the line set can be used over.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,873
    Quote Originally Posted by beenthere View Post
    Thats not true. Lots of old line sets are still the correct size for new systems.

    While I prefer to change the line set. It is not actually required in many applications.


    OP: Do you know what size your line set is? If so, could you please post it. Along with the size of the new proposed unit.
    Beat me to it.
    I've seen lots of older installs, from back in the day, when people really did try to do it right.
    He could be the contractor, that knows his stuff.

  9. #9
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,081
    Some 13 SEER 5 ton R410A units have less capacity loss on a 3/8 X 7/8" X 50' (factory listed size) line set then an R22 unit.

    Some techs are not aware that R410A is suppose to have a higher vapor velocity then R22 for good oil return.

    R22 vertical riser 1000 FPM (From York piping guide)
    R410A vertical riser 1250 FPM (From York piping guide)

    The application (individual install parameters) determine line set size.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #10
    Join Date
    Jul 2009
    Posts
    51
    I noticed that most suction lines are one size larger for R22 than 410a. For example, a 3 ton R22 would have a 7/8" line and a 410a might have a 3/4" line. Is there any problem with going up one size on the suction line?

  11. #11
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,081
    Varies with the individual install application.

    No one answer fits all applications.


    To get the whole answer to this and many other technical questions.

    If your in the trade, get your post count up to 15.
    Then use this link Apply for Pro Membership and apply for Pro Membership.

    Once accepted, you have access to the pro tech forums. Where you can ask and get answers to technical questions.

    Plus, you also have access to the Pro Educational Forums.

    All of it is free.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #12
    It will be a 4 ton 14 seer R410a unit. I'll have to check the line set size. I have to believe this will be the fourth condensing unit hooked up to this line set if it's re-used.

  13. #13
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,081
    Quote Originally Posted by maddog82 View Post
    It will be a 4 ton 14 seer R410a unit. I'll have to check the line set size. I have to believe this will be the fourth condensing unit hooked up to this line set if it's re-used.
    Look at any contract, or written proposal you have or receive.
    Does it say 14 SEER condenser?
    Or, does it say 14 SEER system?

    Matched to the correct indoor unit. A 13 SEER condenser, can reach 14 SEER and or higher. But still use the same line set size as a 13 SEER condenser.

    There is a lot more to it, then just what refrigerant is being used.

    Post the line set size.
    The line set total length.
    Condenser above or below indoor unit.
    How much height difference.
    Brand of equipment.
    Model numbers of equipment.

    This is the info that is generally needed (and easily gotten) for a contractor to determine what size line set is needed for an install. So a contractor on site, is generally able to better determine what size to use. Instead of us looking through our monitors.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event