Entering Fluid Temp, SHR and ADP heat pump
Looking at a water heat pump spec sheet
CAPACITY DATA (all performance at 650 CFM and 5.0 GPM)
COOLING 50°F to 100°F
Trying to figure out the following info:
Entering Fluid Temp. (50 °F)
Entering Air Temp. (DB: 75°F and WB: 63°F)
Total Cap.: 20.53 MBTU/h
Sensible Cap.: 15.00 MBTU/h
SHR: 0.73
Graphically I find an ADP of 46°F. How can that be? If my ADP is 46°F, The fluid temp should be even lower no?
-
09-07-2009, 01:58 PM #2
Redo your calcs. I think it comes out closer to 56.
-
09-07-2009, 02:40 PM #3
Regular Guest
- Join Date
- Jul 2009
- Posts
- 50
I didn't calculate anything I just pulled a straight line between the SHR and the 100% HR curve crossing the entering air value (DB, WB)
-
09-07-2009, 02:55 PM #4
Sorry. I meant you'll find that the dew point of your air at those temp conditions is 56°F.
-
09-07-2009, 03:44 PM #5
Regular Guest
- Join Date
- Jul 2009
- Posts
- 50
I understand the dew point is 56°F for that given value.
But isn’t the “entering fluid temp” the temperature inside the evaporator? Therefore more or less the ADP?
-
09-07-2009, 05:07 PM #6
The water/fluid temp isn't your actual ADP temp. The coil is still warmer yet.
This may or may not help you.