    Entering Fluid Temp, SHR and ADP heat pump

    Looking at a water heat pump spec sheet

    CAPACITY DATA (all performance at 650 CFM and 5.0 GPM)
    COOLING 50°F to 100°F

    Trying to figure out the following info:

    Entering Fluid Temp. (50 °F)
    Entering Air Temp. (DB: 75°F and WB: 63°F)

    Total Cap.: 20.53 MBTU/h
    Sensible Cap.: 15.00 MBTU/h
    SHR: 0.73

    Graphically I find an ADP of 46°F. How can that be? If my ADP is 46°F, The fluid temp should be even lower no?

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,520
    Redo your calcs. I think it comes out closer to 56.
    Contractor locator map

    How many times must one fix something before it is fixed?

  3. #3
    I didn't calculate anything I just pulled a straight line between the SHR and the 100% HR curve crossing the entering air value (DB, WB)

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,520
    Sorry. I meant you'll find that the dew point of your air at those temp conditions is 56°F.
    Contractor locator map

    How many times must one fix something before it is fixed?

  5. #5
    I understand the dew point is 56°F for that given value.

    But isn’t the “entering fluid temp” the temperature inside the evaporator? Therefore more or less the ADP?

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,520
    The water/fluid temp isn't your actual ADP temp. The coil is still warmer yet.

    This may or may not help you.
    Contractor locator map

    How many times must one fix something before it is fixed?