Replacing a 25 yr-old System in a 3 Story Old Victorian
Results 1 to 2 of 2
  1. #1

    Question Replacing a 25 yr-old System in a 3 Story Old Victorian

    I am replacing a "single unit" ( 1 condensor - 1 furnace) 8 SEER and 55% efficient furnace. I have gotten multiple bids but would like some opinions.

    House Information: Hardwood throughout, most walls are insulated. I also have a unconditioned basement. Located in St. Louis.

    1-bid: 1 3-Ton 14 SEER condenser for the 1st and 2nd floor with a 75k BTU 92% Furnace. 1 3-Ton 14 SEER condenser for the 2nd and 3rd floor with a second 75k BTU 92% furnace. New duct work for 2nd and 3rd floor. All Equipment is Ducane

    2-bid: 1 3-Ton 16 SEER condenser for the 1st and 2nd floor with a 90k BTU 95% Furnace. 1 3-Ton 13 SEER condenser for the 2nd and 3rd floor with a 15kW air handler. New duct work for 2nd and 3rd floor. All Equipment is Goodman.

    All costs are the same and is not issue, Any suggestions?
    Thanks

  2. #2
    Join Date
    May 2009
    Posts
    196
    Old, multi story, houses are very hard to heat and cool effectively. Doing the all the design math is essential.

    Did either bidder do a room-by-room Manual J load calculation? Manual D duct sizing calculation? Manual S equipment sizing? If not, ditch the bids and keep looking for a contractor who's prepared to do the job right.


    You're on the right track to install two systems. They just have to be sized properly.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event