Tankless CO readings
after replacing a leaking pipe adapter on a Navien cr-180 tankless unit today, i decided to take some CO readings at the termination. With the kitchen tap running only, I got a CO reading of 115 PPM. Firing rate was about, 110,000 btu's. My own Rinnai tankless unit with the bathroom tap running, produced 55PPM and firing at about 90, 000 Btu's. Should there be any concern regarding these readings, or are they fairly normal. Gas piping is all to code. Any areas to look over again??
-
09-05-2009, 07:14 PM #2
Professional Member*
- Join Date
- Dec 2000
- Location
- Michigan
- Posts
- 723
Combustion Air
Open a window and run the test!
I have received many calls on Tankless water heaters backdraftingThe quality of my performance, sometimes depends on the quality of my audience.
Imitation (Plagiarism) is the best compliment one can get -- "Open A Window"
To improve Indoor Air Quality: Control Indoor Air QUANTITY = "I.A.Q.Q."
-
09-05-2009, 07:17 PM #3
Professional Member*
- Join Date
- Jul 2009
- Location
- Ontario, Canada
- Posts
- 902
-
09-05-2009, 08:07 PM #4
Regular Guest
- Join Date
- Jan 2009
- Location
- Sterling Heights, MI
- Posts
- 60
If everything is hooked up correctly how would CO be coming into the house? Where is it coming from?
-
09-05-2009, 08:11 PM #5
Professional Member*
- Join Date
- Jul 2009
- Location
- Ontario, Canada
- Posts
- 902
-
09-05-2009, 11:19 PM #6
readings to 150ppm are considered within spec. If you need documentation for NYSERDA, Honeywell, CSG or BPI standards contact me.
Which makes more sense to you?
CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%
DO THE NUMBERS! Step on a HOMESCALE.
What is comfort? Well, it AIN'T just TEMPERATURE!
Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.
-
09-06-2009, 08:40 AM #7
You only took one set of readings.
There is no way to gauge the safety of that equipment with only one set of readings.
You will need multiple readings over the entire run cycle to determine whether it's safe or not.
I would look long and hard at any readings over 100 PPM as read for a potential issue.Have you set up a Google alert for Carbon Monoxide yet?
Click here to find out how.
-
09-06-2009, 08:42 AM #8Have you set up a Google alert for Carbon Monoxide yet?