Results 1 to 10 of 10
    Jun 2009
    StL, MO
    McQuay / Thieves / Mucho work
    This one is from last summer. We get a call a week before school starts - "Thieves stole our a/c piping, can you give us a price to replace it?" It turns out we were the only ones to respond.
    One look at this sign and we should have run.
    Attachment 46752
    This is what we found. Hot gas and liquid lines are broken off at the building and the condenser headers are gone. FWIW, this is a McQuay 220 ton air cooled condenser.
    Attachment 46762
    Attachment 46772
    First, the coil had to be supported and then we chopped, sawed, hacked the tubes down to the tube sheet.
    Attachment 46782
    Then we removed the tube sheets (which also support the condenser fans) and peeled away enough fins to work with the tubes. The new hot gas headers are almost done.
    Attachment 46792
    This is pretty much what we ended up with.
    Attachment 46802
    UA LU 562
    lancaster ca
    wow seems like alot of work looks good
    Western MA.
    Not criticizing your work,which is very nice,but was replacing the whole condenser an option?
    I love overtime I just hate working for it.
    Yea, that thing looks a bit on the ancient side
    a 220 ton condenser is probably worth fixing, even to that extent
    Jun 2009
    StL, MO
    houtonjr - thanks
    sirjames - thanks. Fixing it was the only real option as a new condenser that would fit on the pad (and inside the brick walls) was 8 to 10 weeks lead time - they would have been out of the cooling season by then.
    BaldLoonie - the condenser was seven years old at the time.
    cody350 - yep
    UA LU 562
    South Carolina
    I think you guys did a great job!! I likes to braze all that stuff- fun
    So did you have to unbraze all that new piping to get the tube sheet back on?
    Seriously, I'm curious to see how the finished product came out... Did you have new stainless tube sheets and panels made up?
    Nice work, well done. I bet the customer was happy, too.
    Jun 2009
    StL, MO
    papa jo - thanks.
    BergerMech Rob - thanks. McQuay didn't swage the tubes in the tube sheet. I believe "floating tube sheet" is the jargon. That end of the coil is now supported from below by the uni-strut seen in the last three pictures. We had our shop shear the original tube sheets and put a 90° bend the on the bottom to stiffen the sheet. The sheets were needed to support the condenser fans.
    For some reason we didn't snap a pic of the finished product. The photos were taken at the end of each day to verify the work in progress. We were afraid the thieves might hit us before the work was complete and payment would become an issue.
    I don't know about the bookkeepers, but the teachers were estatic.
    UA LU 562
    Jun 2001
    Michigan
    those sorts of repair jobs you remember over the years. Great Job. The only think is the drop leg outlet. That should street 90 down right out of the manifold.