Thread: leibert 20 ton unit shorted to ground

  1. #1
    Join Date
    Feb 2007
    Posts
    20
    Post Likes

    leibert 20 ton unit shorted to ground

    Hey all. I can't believe I'm asking this, but I just want to make sure. I have a Carlyle compressor in a Leibert 20 ton unit. Blown contactor and fuses. I've got correct Ohms between legs, but I also have Continuity to ground on each leg. I know this isn't right, but is it common to have a short to ground on every leg; Or am I missing something.

  2. #2
    Join Date
    Jul 2006
    Location
    Brooklyn , NY
    Posts
    24
    Post Likes
    Quote Originally Posted by jim4237 View Post
    I know this isn't right, but is it common to have a short to ground on every leg; Or am I missing something.
    Yes, its common for 3 phase motor,
    if one leg short to ground other short too.


  3. #3
    Join Date
    Nov 2008
    Posts
    1,673
    Post Likes
    Did the first leg to short cause the other two shorts?

  4. #4
    Join Date
    Jun 2008
    Location
    Apopka, Florida
    Posts
    110
    Post Likes
    Quote Originally Posted by jim4237 View Post
    Hey all. I can't believe I'm asking this, but I just want to make sure. I have a Carlyle compressor in a Leibert 20 ton unit. Blown contactor and fuses. I've got correct Ohms between legs, but I also have Continuity to ground on each leg. I know this isn't right, but is it common to have a short to ground on every leg; Or am I missing something.
    Jim,

    When you say a blown contactor, What do you mean?

    I have seen many a circumsatnce that technicians do not change badly pitted contactors and then what to know why they lost a compressor. When it was obvious that the contacts welded together and ran the compressor into oblivion or unitil she just shot the bed. Because of a 30 dollar part the lost a 4000 dollar compressor, it just don't make sense.

    But it is common for the high voltage to short together, to ground, or too the internal overload which would cause more damage running high voltage thru the control circuits.

    Domcort

  5. #5
    Join Date
    May 2008
    Location
    Woodhaven, Michigan, United States
    Posts
    58
    Post Likes
    yes it would be all three if melted contacts but im surprised there isnt any open windings then at least one

  6. #6
    Join Date
    Feb 2007
    Posts
    20
    Post Likes
    Thread Starter

    short

    I was testing fire alarms and it shunt tripped the hvac units. After resetting breakers I noticed it was getting hot in space. The contactor on compressor 1 was fried; burnt wires, etc. I replaced contactor and fuses and restarted without checking motor. It blew all the fuses again immediately. Seems like L3 fuse was hotter than the other 2 legs. Isolated motor and OHM'd out each leg to ground and got resistance on each. And also got resistance between each leg.

  7. #7
    Join Date
    Jun 2008
    Location
    Apopka, Florida
    Posts
    110
    Post Likes
    Quote Originally Posted by jim4237 View Post
    I was testing fire alarms and it shunt tripped the hvac units. After resetting breakers I noticed it was getting hot in space. The contactor on compressor 1 was fried; burnt wires, etc. I replaced contactor and fuses and restarted without checking motor. It blew all the fuses again immediately. Seems like L3 fuse was hotter than the other 2 legs. Isolated motor and OHM'd out each leg to ground and got resistance on each. And also got resistance between each leg.
    Jim,

    Burnt wiring, smybolizies that there may have been a loose connection(s).

    Anything can happen internally to the compressor, shorting phase to phase and then to ground can happen, shorting high voltage to the internal overload can also happen, which is low voltage.

    Looks like a replacement compressor is needed, if you have the original compressor rebuilt you may get a better understanding of whta happened internally.

    keep us posted,
    Domcort

  8. #8
    Join Date
    Nov 2008
    Posts
    1,673
    Post Likes
    Quote Originally Posted by Domcort View Post
    Burnt wiring, smybolizies that there may have been a loose connection(s).
    if it's within a few inches of the connection. Crispy the whole length means overload.

  9. #9
    Join Date
    Jun 2008
    Location
    Apopka, Florida
    Posts
    110
    Post Likes
    Quote Originally Posted by WhoIsThat? View Post
    if it's within a few inches of the connection. Crispy the whole length means overload.
    I would agree with that, the fuses protect the wiring and the device i.e, the load.

    Domcort

  10. #10
    Join Date
    Nov 2008
    Posts
    1,673
    Post Likes
    20A through a bad connection having 0.02 Ω contact resistance is 8 W. If the connection has a small surface area [e.g., that of a pea] it will get very hot.

    I had a half volt drop @10A through a badly installed wirenut connection. I was pulling 10A to check for bad connections just like this one.

  11. #11
    Join Date
    Jan 2009
    Location
    Paradise, NL, Canada
    Posts
    43
    Post Likes
    Disconnect the wires from the compressor terminals and check there to rule out an external wiring or contactor problem. I would bet the compressor is toast.

  12. #12
    Join Date
    Apr 2003
    Location
    the Great Pacific Northwest
    Posts
    607
    Post Likes
    Quote Originally Posted by jim4237 View Post
    Hey all. I can't believe I'm asking this, but I just want to make sure. I have a Carlyle compressor in a Leibert 20 ton unit. Blown contactor and fuses. I've got correct Ohms between legs, but I also have Continuity to ground on each leg. I know this isn't right, but is it common to have a short to ground on every leg; Or am I missing something.
    Just to clarify, the short to ground is most likely or could be at just one location or area of on of the three independent windings of the motor. the motor windings are connected internally at each of the power connestions, if you were to designate the windings with letters as A,B,C, then terminal 1 would have the " input" lead of winding A and the "output" of winding C connected to it,terminal 2 would have the " input" lead of winding B and the "output" of winding A connected to it, terminal 3 would have the " input" lead of winding C and the "output" of winding B connected to it.

    Therefore, if the short to ground is anywhere in the motor you will read it on all three motor terminals.

    Hope this helps.

  13. #13
    Join Date
    Jan 2007
    Location
    Charm City--the city that bleeds
    Posts
    2,788
    Post Likes
    when you say "continuity to ground", do you mean low resistance?
    Typically if your standard multimeter is ringing to ground then yes, it's gone. But, I'm just looking for you to clarify a bit.

    What are the values of each leg to ground?

    Are you talking like Megohms or are you talking 10, or 800, or 27K ohms?
    It's great to be alive and pumping oxygen!

  14. #14
    Join Date
    Nov 2003
    Location
    Montreal, Qc.
    Posts
    917
    Post Likes
    Before condeming any semi hermetic due to a suspected short circuit I remove the terminal plate and disconnect the wires to test the windings with a megger.
    The service valves must be front seated and the refrigerant recovered from the crankcase prior to removing the terminal plate.

    Carlyle Service Guide

    From the Thermacon Compressor Guide

    Compressor Testing Guide
    Please use this guide if you suspect a faulty compressor
    To verify basic compressor function in a field environment the following will
    demonstrate whether further investigation will be necessary or not.
    1 Earth Test Using a 1000v Megger check each field winding
    to earth. 1st check the earth connection is
    sound by an earth to earth test & repeat this
    following the motor test.

    If reading < than 2 MÙ Stator probably burnt out,
    but do not rule out a contaminated / damp
    terminal plate.

    Reading 2 MÙ - 20 MÙ Probably not burnt out, terminal plate
    contaminated or damp.
    Separate terminal plate from main casting &
    repeat check to casting. If fault clears then
    terminal plate is faulty.

    Reading > 20 MÙ No earth Fault

    Precautions Do not effect Megger checks under deep vacuum.
    Do not Megger overloads.

    2 Field Balance Using an Ohmmeter set on Ohms verify balance
    3ø motors only of motor field coils.
    If balance is out by more than 10 % suspect
    motor is defective.
    Separate terminal plate & repeat measurements,
    if readings do not improve rewind is probably
    required.

  15. #15
    Join Date
    Jan 2008
    Location
    pritzberg
    Posts
    4,641
    Post Likes
    great procedure thumper

  16. #16
    Join Date
    Nov 2003
    Location
    Montreal, Qc.
    Posts
    917
    Post Likes
    Quote Originally Posted by heavymetaldad View Post
    great procedure thumper
    Thanks, and get well soon.

  17. #17
    Join Date
    Jul 2006
    Location
    Brooklyn , NY
    Posts
    24
    Post Likes
    Application Engineering Bulletin
    AE-1294 August 1, 1992

    MEGOHM VALUES OF COPELAND COMPRESSORS

    ......There are many factors that affect megohm
    readings including contaminated refrigerant, oil
    level, refrigerant in oil and current leakage through
    electrical fusites or terminal plates.

    Any external electrical components connected to
    the compressor terminals also affect megohm readings.
    Wires, contactors and relays all leak current
    and will decrease compressor megohmeter readings
    if not disconnected.

    As mentioned earlier a single megohm reading
    cannot be used to condemn a compressor since
    many other factors are involved. However, limits can
    be placed on megohm values that dictate action be
    taken. Copeland has found that these limits are
    related to the rated voltage of the compressor. Megohm
    values equal to or greater than 1000 ohms per
    volt are probably acceptable. For example, a 460 volt
    compressor might show a megohm reading of 460,000
    ohms or 0.46 megohm. Compressors with rated
    voltages of 208 to 230 volts would then be operable
    at megohm values of 0.208 to 0.230 megohms; for
    simplicity, Copeland has set the limit at 0.5 megohms
    before a compressor is condemned.

  18. #18
    Join Date
    May 2004
    Location
    Sunny Mid South
    Posts
    508
    Post Likes
    Quote Originally Posted by valentyn View Post
    Application Engineering Bulletin
    AE-1294 August 1, 1992

    MEGOHM VALUES OF COPELAND COMPRESSORS

    ......There are many factors that affect megohm
    readings including contaminated refrigerant, oil
    level, refrigerant in oil and current leakage through
    electrical fusites or terminal plates.

    Any external electrical components connected to
    the compressor terminals also affect megohm readings.
    Wires, contactors and relays all leak current
    and will decrease compressor megohmeter readings
    if not disconnected.

    As mentioned earlier a single megohm reading
    cannot be used to condemn a compressor since
    many other factors are involved. However, limits can
    be placed on megohm values that dictate action be
    taken. Copeland has found that these limits are
    related to the rated voltage of the compressor. Megohm
    values equal to or greater than 1000 ohms per
    volt are probably acceptable. For example, a 460 volt
    compressor might show a megohm reading of 460,000
    ohms or 0.46 megohm. Compressors with rated
    voltages of 208 to 230 volts would then be operable
    at megohm values of 0.208 to 0.230 megohms; for
    simplicity, Copeland has set the limit at 0.5 megohms
    before a compressor is condemned.
    Thanks! I bought a megger a few months ago. Hadn't had a chance to figure out how to use it. This helps me get a feel for it. This thread is long out of play, so don't know if it will be seen, but what Megger setting recommended?
    -Surf Life Hard!!!-

  19. #19
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    smell the freon off the suction it went NUKE..your cooked
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  20. #20
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    moved thread to Tech to Tech commercial



+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •