    [QUOTE=ChillerWisperer;4635092]What empirical data do you base your facts on, or is it just an opinion based on anecdotal observations and hearsay evidence?[/QUOTE


    I'm fine with opinion in this case. I certainly wouldnt go to an internet message board if I was seeking specific facts. I just want to see if there is a brand that is clearly preferred. If 78 of 100 all see that "X" brand is best; there's usually a reason.

  2. #54
    Join Date
    May 2007
    Location
    Surrey BC
    Posts
    118
    Quote Originally Posted by ChillerWisperer View Post
    R-123 isn't scheduled for phaseout until January 2030

    http://www2.dupont.com/Refrigerants/..._phaseout.html

    Recently the japs version of AC/R News (JARN) interviewed Dr. Stephen Andersen of the EPA and his comments highlight the phaseout of R-134A prior to R-123. He points out that even though 123 has a greater ODP, it is a moot point because chillers using it are zero emission. With sufficient quantities being manufactured until 2030 and the fact that very little is lost during normal operation and maintenance, there will be plenty of 123 for years to come after 2030. In addition to that, the EPA will let manufacturers of 123 produce beyond the 2030 phaseout by using ODP unit credits gained by the conversion or decomissioning of R-11 chillers and destroying the R-11. For every two pounds of 11 destroyed, they can produce one pound of 123.

    I think Trane made the right gamble by sticking with R-123. They are now the sole manufacturers of a low pressure machine that will likely outlast a lot of the 134A machines being produced by York, Carrier and McQuay. Add to that the inherent efficiency advantage over 134A and it should give them dominance in the market.

    I wish I could attach the article here, but it's about 3mb in pdf format. If anyone wants it, let me know and I will email it to you.
    Could you please send me a copy of this article?

  3. #55
    Join Date
    Jun 2009
    Location
    Florida
    Posts
    540
    Quote Originally Posted by kwhit View Post
    Could you please send me a copy of this article?
    Done! Please feel free to share your opinions and thoughts after you read it.
    Low Pressure Forever!

    If you know heavy metal, you can work anywhere-Dave Andreson

    Anchors Aweigh my boys, Anchors Aweigh!
    Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!

  4. #56
    Join Date
    Apr 2004
    Location
    Lombard, IL
    Posts
    29
    TRANE,TRANE,TRANE,TRANE. Best chillers in the country. R123 going away might happen, might not, my guess is not. We are still producing it selling it and plan to keep on selling it. Bottom line is if you want a great chiller buy a trane.

  5. #57
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,059
    the rtaa.,cvhe and f., all the way

  6. #58
    Join Date
    Jul 2008
    Location
    syracuse Ny
    Posts
    84
    the german brand you might be refering to is Bitzer. Right now they are starting to produce them right in Syracuse NY, Right down the road from Carrier designed by some of the same people who designed carriers units.

  7. #59
    Join Date
    Jun 2009
    Posts
    3
    Quote Originally Posted by ice_cube_30 View Post
    TRANE,TRANE,TRANE,TRANE. Best chillers in the country. R123 going away might happen, might not, my guess is not. We are still producing it selling it and plan to keep on selling it. Bottom line is if you want a great chiller buy a trane.
    R-123 is a great refrigerant, but it's going away.

  8. #60
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    1,817
    At least Trane doesn't have a shaft seal that you have to wrestle the local OEM office for the part number of. But I bet they sell 75 dollar a gallon Oil 22 that is really 4GS.
    God Bless our Veterans

    God Bless the USA

  9. #61
    Join Date
    Sep 2006
    Posts
    57
    There are pro's and con's to all machines. At my previous job, which was at a semiconductor plant for 15 years, I was responsible for all repairs, and maintenance of 27 centrifugals. Carrier 19XL,19EX, Trane CVHE, CVHF, and York YT, 450 ton thru 2000 ton. We also had 30 or so 200-400 ton screws, McQuay ALSA, Mycom 60's, and Trane RTAA, and RTAC. The only destructive failure I had in those 15 yrs was the Trane CVHE1250 ton which had a rotor bar issue, which has been an issue for Trane. As run hours increased open and inspects began on all. All but one of the Carriers had bearings out of spec after 25K-30K run hours. The 19EX mostly had issues with condenser tube failures. We had the most compressor failures on the ALS A vintage for obvious reasons, and RTAA's that we used on a 0 degree F glycol system. The latest additions to the plant just prior to me leaving 2 yrs ago were two Trane CVHF1750 chillers. Great KW/ton, but on one of them the fluid pump was seized on start up, and that machine has had two thrust bearings replaced since start up 2 years ago. One by Trane techs while labor was in warranty, and the second by in house tech. The York YT's, even with the latest greatest bellows shaft seal configuration still have issues with leaks, but they do great with low condenser water temps, and are simple to overhaul. R123 is going away, but don't underestimate the lobbyists to keep it around as long as possible.

  10. #62
    Join Date
    Feb 2010
    Posts
    4
    I've just joined, so forgive me if this has been mentioned but in the UK it is now illegal to use virgin R123 and only recycled R123 is allowed for topping up systems. This has been the case since January 2010.

  11. #63
    Join Date
    Feb 2010
    Posts
    1

    Smile help needed

    I hope someone can assist me with the following:

    We are in South Africa and absorption chillers are still very new for us.

    Could you possibly advise me on any good and bad experience you have had with absorption chillers with lithium bromide?

    As there are a few companies to choose from (Broad, Trane, York, Sanyo), we are not sure how to go about choosing a company, what suggestions would you make?

    What are the most common problems experienced with these products?


    Thanks

  12. #64
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,609
    Quote Originally Posted by minimoose View Post
    I hope someone can assist me with the following:

    We are in South Africa and absorption chillers are still very new for us.

    Could you possibly advise me on any good and bad experience you have had with absorption chillers with lithium bromide?

    As there are a few companies to choose from (Broad, Trane, York, Sanyo), we are not sure how to go about choosing a company, what suggestions would you make?

    What are the most common problems experienced with these products?


    Thanks
    You probably need to start a thread with this question as the topic if you want as much response as possible.

    As far as absorbers, they're like anything else - there's good and bad to all. I don't have a lot of personal experience with anything other than the York machines, and they do pretty well, especially the 2 stage. No matter who builds it, an absorber is maintenance intensive, but if you look after them and keep them tight, they'll last a long time and make a lot of cold water. If you learn what makes 'em tick, they're really good as a source of job security, too.

Page 5 of 5 FirstFirst 12345

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event