Results 1 to 9 of 9
    Greater Boston Area
    Trane RTAC 200 - Noise expectations
    I am looking for a typical dB rating for this chiller. I have been unable to find anything being published from Trane.
    Thank you,
    ottawa canada
    I dont know about the Db ratings but I wouldnt install one in a noise sensitive area without the sound blanket option . They are a PITA for service but make a huge noise difference . Also follow the installation guidlines . "NO BRAIDED PIPING ISOLATERS" and dont hang the piping on the chiller frame .
    Nov 2008
    That can be found in the submittal data provided by the Trane New System Salesman.
    Indiana
    Don't know the db rating but keep in mind that a remote evp is much more noisy than a package unit. Haven't found the solution for that yet, it seems to be a harmonic problem.
    Aug 2009
    Scranton Pa
    I actually have a submittal at my office for that exact machine with the ratings. They're no louder than any other 200 ton air cooled screw screamer. I can scan it in and post it tomorrow morning. Its rejected BTW lol. Not because of the sound, because it doesn't operate as well as a Carrier 30XA with variable primary and required an additional 200 amps of breaker capacity.
    If you need an air cooled machine, and it is a sound sensitive scenario, definitly use the blankets and low sound fans, but look into a barrier, as provided by AcoustiBlok or Kinetics.
    Aug 2009
    Scranton Pa
    RTAC Sound Pressure
    Boston,
    See attached for equipment sound power. You'll have to convert it to sound pressure based on the distance from the machine.
    Greater Boston Area
    Thumbs up Thank you for all of your input.
    Thanks again.
    North Carolina
    Quote Originally Posted by FlewtheCoop View Post
    The York YCIV is a whole lot less noisy than the Trane RTAC. Have several of each under contract.
    Jun 2007
    Here. I'm right here i tell you!
    Quote Originally Posted by chad_nc View Post
    Its even less noisy when silent night mode is active. Of course you can only get up to about 60 percent in that mode before it reverts back to the normal operating mode.