Trane chiller
I am installing a RTWA 125 ton used chiller and was wondering if it matters whitch way the condincing water flowes and if you can move the crossover tube that connects the two barrowes to the other side Thanks Dan
-
07-09-2012, 01:10 PM #2
Hi
check the instalation manual that came with the unit.
if i remember it shouldnt be a problem but that depends on site
you would have to move the sensors to .
check with a trane rep to be 100 % sure
good luck
-
07-09-2012, 04:47 PM #3
Professional Member
- Join Date
- Sep 2008
- Location
- A land down under
- Posts
- 285
For RTWA the counterflow subcooler design requires non-interchangeable waterboxes so if you want it to work correctly water connections are right side when facing the control panel - direction of flow is also critical for unit performance. Refer pages 18-21 of attached.