  1. #1
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793

    Tower water temps

    Looking for a little chiller help... I have a Carrier 30HR050-B150 with water IN from the tower at 110 degrees and leaving the chiller at 122 degrees. The outside temp was 98 yesterday. How much of a delta should I expect to see? The water leaving the chiller was only 52 degrees.
    Last edited by air2spare; 08-27-2009 at 12:37 PM.

  2. #2
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,712
    Why was your tower water so hot should be about 85 or so?
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  3. #3
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    Quote Originally Posted by thegoodlistener View Post
    Why was your tower water so hot should be about 85 or so?
    I'm thinking something is restricting water flow or a weak pump, I really have no way of determining GPM

  4. #4
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,712
    Your delta T is not too bad could be alittle better but your condenser water loop is not transfering much heat from what I can tell.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  5. #5
    Join Date
    Aug 2006
    Location
    Columbus Ohio
    Posts
    1,985
    Whow! Tower loop is way way way too hot. You need to confirm the tower and tower fan are in good working order before you do anything else. Then check your pumps, pull strainers, check circuit setters, and lastly condenser barrel water pressure controls if you have them.

    I suspect you either have flow issues or your tower fan is not working.
    UA LU189

    10mm, because it's better than .45acp

  6. #6
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    the fan appears to be fine but I did notice alot of algae in the tower

  7. #7
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    is the water treatment best left to a 3rd party to maintain?

  8. #8
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,712
    Quote Originally Posted by air2spare View Post
    is the water treatment best left to a 3rd party to maintain?
    Yes it would in my opinion. Does there appear to be a sufficient flow in the tower ?
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  9. #9
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    not really. is there a method for measuring GPM w/o a flow meter?

  10. #10
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,712
    You need the PD across the heatexchanger. Then you will have to know the performance curve for that model chiller .At least that is how I do it other people may have a better way of doing it.
    Ifyou shoot me a M# I will try to find something on it.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  11. #11
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    the M# is on the first post, thanks

  12. #12
    Join Date
    Oct 2006
    Location
    Central Texas
    Posts
    633
    What kind of tower do you have? Is water going over the top of the tower? Or maybe running through a bypass? Hot deck plugged up? 110*h20 pretty darn hot. Not to sound like an a$$ but is the fan going the right direction?
    Sic Semper Tyrannis.

  13. #13
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,609
    "Lots of algae" will cause the tower not to make capacity. Based on rule of thumb, your condenser delta T looks good (should go down when problem is corrected) assuming you're at full load, but you're not removing the heat from the cooling water. Your tower ain't makin' capacity......

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event