Thread: Tower water temps
-
08-27-2009, 09:51 AM #1
Professional Member
- Join Date
- Sep 2005
- Location
- Texas
- Posts
- 2,793
Tower water temps
Looking for a little chiller help... I have a Carrier 30HR050-B150 with water IN from the tower at 110 degrees and leaving the chiller at 122 degrees. The outside temp was 98 yesterday. How much of a delta should I expect to see? The water leaving the chiller was only 52 degrees.
Last edited by air2spare; 08-27-2009 at 12:37 PM.
-
08-27-2009, 10:17 AM #2
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,512
Why was your tower water so hot should be about 85 or so?
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
08-27-2009, 11:22 AM #3
Professional Member
- Join Date
- Sep 2005
- Location
- Texas
- Posts
- 2,793
-
08-27-2009, 11:26 AM #4
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,512
Your delta T is not too bad could be alittle better but your condenser water loop is not transfering much heat from what I can tell.
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
08-27-2009, 11:42 AM #5
Whow! Tower loop is way way way too hot. You need to confirm the tower and tower fan are in good working order before you do anything else. Then check your pumps, pull strainers, check circuit setters, and lastly condenser barrel water pressure controls if you have them.
I suspect you either have flow issues or your tower fan is not working.UA LU189
10mm, because it's better than .45acp
-
08-27-2009, 12:02 PM #6
Professional Member
- Join Date
- Sep 2005
- Location
- Texas
- Posts
- 2,793
the fan appears to be fine but I did notice alot of algae in the tower
-
08-27-2009, 12:04 PM #7
Professional Member
- Join Date
- Sep 2005
- Location
- Texas
- Posts
- 2,793
is the water treatment best left to a 3rd party to maintain?
-
08-27-2009, 12:24 PM #8
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,512
-
08-27-2009, 12:30 PM #9
Professional Member
- Join Date
- Sep 2005
- Location
- Texas
- Posts
- 2,793
not really. is there a method for measuring GPM w/o a flow meter?
-
08-27-2009, 12:34 PM #10
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,512
You need the PD across the heatexchanger. Then you will have to know the performance curve for that model chiller .At least that is how I do it other people may have a better way of doing it.
Ifyou shoot me a M# I will try to find something on it.UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
08-27-2009, 12:38 PM #11
Professional Member
- Join Date
- Sep 2005
- Location
- Texas
- Posts
- 2,793
the M# is on the first post, thanks
-
08-27-2009, 09:26 PM #12
What kind of tower do you have? Is water going over the top of the tower? Or maybe running through a bypass? Hot deck plugged up? 110*h20 pretty darn hot. Not to sound like an a$$ but is the fan going the right direction?
Sic Semper Tyrannis.
-
08-27-2009, 09:56 PM #13
Professional Member*
- Join Date
- Dec 2008
- Location
- Dixiana, AL
- Posts
- 2,487
"Lots of algae" will cause the tower not to make capacity. Based on rule of thumb, your condenser delta T looks good (should go down when problem is corrected) assuming you're at full load, but you're not removing the heat from the cooling water. Your tower ain't makin' capacity......