    I recentley replaced a large 35HP compressor and also replaced the suciton drier cores. I gave my local dist the # on the can for both the suction and liquid cores- said the same for both. When i replaced the suction cores I found them to be pleated paper elements rather then the desicants like a liquid drier, thought to myself well thats what i was told, so i put the desicant liquid drier cores in the suction canister, is that ok and can I mess something up in doing so? I later was told that the pleateds should go in there from the same dist- go figure. Also was wondering if i need to change the suction core when changing the liquid line cores. Should they (suction) be changed also even if theres no obvious sign of restricion (psi/temp drop ect. )there. My gut says yes but $ a real issue for the customer (Like its not always but ya know).
    Apr 2001
    Quote Originally Posted by dave1234 View Post
    If it's a Sporlan RC-4864 core, it is the standard core suitable for both liquid and suction line applications.
    Jabs
    Ohio
    Suction line cores will break down over time and get into the system. The longest I will leave tem in for is around 30 days to clean up the system, then they are removed and pleated filters are put in.
    florida
    Quote Originally Posted by zw17 View Post
    Just leave them out after 30 day's.
    Educational forums are open.
    I've seen those pleated filters come apart and get into the system. I have found fibers from it in the TXV screen before. I leave em out.
    Jul 2009
    texas
    sporlan
    sporlan says the [suction]dessicants are for clean up only and not the same as the typical rc-4864 and should be used for a short time and to put a felt in for long term i takem out as personal prefrence
    Quote Originally Posted by cletus31 View Post
    What is a felt? So there is a difference between a "suction core" and the pleated filter cores?
    Apr 2002
    Dallas, TX
    A filter-drier core is the same for liquid or suction.
    http://sporlan.jandrewschoen.com/40-10.htm
    Felt elements should be used in the suction line if you are not cleaning up the system.
    http://sporlan.jandrewschoen.com/80-10.htm
    If the only tool you have is a hammer, you tend to see every problem as a nail. – Abraham Maslow