Results 1 to 8 of 8
  1. #1
    Join Date
    Jul 2008
    Posts
    335

    Suction paper filter drier cores

    I recentley replaced a large 35HP compressor and also replaced the suciton drier cores. I gave my local dist the # on the can for both the suction and liquid cores- said the same for both. When i replaced the suction cores I found them to be pleated paper elements rather then the desicants like a liquid drier, thought to myself well thats what i was told, so i put the desicant liquid drier cores in the suction canister, is that ok and can I mess something up in doing so? I later was told that the pleateds should go in there from the same dist- go figure. Also was wondering if i need to change the suction core when changing the liquid line cores. Should they (suction) be changed also even if theres no obvious sign of restricion (psi/temp drop ect. )there. My gut says yes but $ a real issue for the customer (Like its not always but ya know).

  2. #2
    Join Date
    Apr 2001
    Posts
    669
    Quote Originally Posted by dave1234 View Post
    I recentley replaced a large 35HP compressor and also replaced the suciton drier cores. I gave my local dist the # on the can for both the suction and liquid cores- said the same for both. When i replaced the suction cores I found them to be pleated paper elements rather then the desicants like a liquid drier, thought to myself well thats what i was told, so i put the desicant liquid drier cores in the suction canister, is that ok and can I mess something up in doing so?
    If it's a Sporlan RC-4864 core, it is the standard core suitable for both liquid and suction line applications.

    Jabs

  3. #3
    Join Date
    Aug 2006
    Location
    Columbus Ohio
    Posts
    1,775
    Suction line cores will break down over time and get into the system. The longest I will leave tem in for is around 30 days to clean up the system, then they are removed and pleated filters are put in.
    UA LU189

    10mm, because it's better than .45acp

  4. #4
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,434
    Quote Originally Posted by zw17 View Post
    Suction line cores will break down over time and get into the system. The longest I will leave tem in for is around 30 days to clean up the system, then they are removed and pleated filters are put in.
    Just leave them out after 30 day's.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  5. #5
    Join Date
    May 2004
    Posts
    1,732
    I've seen those pleated filters come apart and get into the system. I have found fibers from it in the TXV screen before. I leave em out.

  6. #6
    Join Date
    Jul 2009
    Location
    texas
    Posts
    49

    sporlan

    sporlan says the [suction]dessicants are for clean up only and not the same as the typical rc-4864 and should be used for a short time and to put a felt in for long term i takem out as personal prefrence

  7. #7
    Join Date
    Jul 2008
    Posts
    335
    Quote Originally Posted by cletus31 View Post
    sporlan says the [suction]dessicants are for clean up only and not the same as the typical rc-4864 and should be used for a short time and to put a felt in for long term i takem out as personal prefrence
    What is a felt? So there is a difference between a "suction core" and the pleated filter cores?

  8. #8
    Join Date
    Apr 2002
    Location
    Ann Arbor, MI
    Posts
    2,945
    Quote Originally Posted by dave1234 View Post
    What is a felt? So there is a difference between a "suction core" and the pleated filter cores?
    A filter-drier core is the same for liquid or suction.

    http://sporlan.jandrewschoen.com/40-10.htm

    Felt elements should be used in the suction line if you are not cleaning up the system.

    http://sporlan.jandrewschoen.com/80-10.htm
    The greater danger for most of us lies not in setting our aim too high and falling short; but in setting our aim too low, and achieving our mark. – Michelangelo

    There are powers inside of you which, if you could discover and use, would make you everything you ever dreamed or imagined you could become. – Orison Swett Marden

    Education is what remains after one has forgotten what one has learned in school. – Albert Einstein

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •