Results 1 to 8 of 8
Thread: Suction paper filter drier cores
-
08-25-2009, 11:51 AM #1
Professional Member
- Join Date
- Jul 2008
- Posts
- 335
Suction paper filter drier cores
I recentley replaced a large 35HP compressor and also replaced the suciton drier cores. I gave my local dist the # on the can for both the suction and liquid cores- said the same for both. When i replaced the suction cores I found them to be pleated paper elements rather then the desicants like a liquid drier, thought to myself well thats what i was told, so i put the desicant liquid drier cores in the suction canister, is that ok and can I mess something up in doing so? I later was told that the pleateds should go in there from the same dist- go figure. Also was wondering if i need to change the suction core when changing the liquid line cores. Should they (suction) be changed also even if theres no obvious sign of restricion (psi/temp drop ect. )there. My gut says yes but $ a real issue for the customer (Like its not always but ya know).
-
08-25-2009, 04:18 PM #2
Regular Guest
- Join Date
- Apr 2001
- Posts
- 669
-
08-25-2009, 04:22 PM #3
Suction line cores will break down over time and get into the system. The longest I will leave tem in for is around 30 days to clean up the system, then they are removed and pleated filters are put in.
UA LU189
10mm, because it's better than .45acp
-
08-25-2009, 08:41 PM #4I love the smell of phosgene first thing in the morning:

To apply for professional membership click here
Educational forums are open.
If you would like to submit a link or an article or other related info to the EF. click here
-
08-25-2009, 08:45 PM #5
Professional Member
- Join Date
- May 2004
- Posts
- 1,732
I've seen those pleated filters come apart and get into the system. I have found fibers from it in the TXV screen before. I leave em out.
-
08-27-2009, 02:59 AM #6
sporlan
sporlan says the [suction]dessicants are for clean up only and not the same as the typical rc-4864 and should be used for a short time and to put a felt in for long term i takem out as personal prefrence
-
08-27-2009, 08:44 AM #7
Professional Member
- Join Date
- Jul 2008
- Posts
- 335
-
08-27-2009, 10:20 PM #8
A filter-drier core is the same for liquid or suction.
http://sporlan.jandrewschoen.com/40-10.htm
Felt elements should be used in the suction line if you are not cleaning up the system.
http://sporlan.jandrewschoen.com/80-10.htmThe greater danger for most of us lies not in setting our aim too high and falling short; but in setting our aim too low, and achieving our mark. – Michelangelo
There are powers inside of you which, if you could discover and use, would make you everything you ever dreamed or imagined you could become. – Orison Swett Marden
Education is what remains after one has forgotten what one has learned in school. – Albert Einstein


Reply With Quote