    the 100 panel has blue read out, only one pressure transducer (oil). one line of display. 200 panel has several lines of display.

  2. #15
    Join Date
    Jun 2009
    Location
    Florida
    Posts
    540
    Ok, it's a 200 panel then.
    Low Pressure Forever!

    If you know heavy metal, you can work anywhere-Dave Andreson

    Anchors Aweigh my boys, Anchors Aweigh!
    Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!

  3. #16
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,135
    this issue ended up being a connection issue right at the MCB. I got a PDF parts file and they don't list a connector kit. Pulled and depressed the connection pin too make it tighter and kept 4.97 vdc input all day. thanks for the input guys.

    r404a

  4. #17
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    1,819
    Way to go!

    I always liked the 200 panel.
    Still have 4 of them on the hoof.
    God Bless our Veterans

    God Bless the USA

  5. #18
    Join Date
    Feb 2003
    Location
    Wichita Ks
    Posts
    1,457
    Quote Originally Posted by r404a View Post
    this issue ended up being a connection issue right at the MCB. I got a PDF parts file and they don't list a connector kit. Pulled and depressed the connection pin too make it tighter and kept 4.97 vdc input all day. thanks for the input guys.

    r404a
    I talked to someone last night said he knows where to get them, I will let you know once I find out.

  6. #19
    Join Date
    Feb 2003
    Location
    Wichita Ks
    Posts
    1,457
    I found some of those red connectors. They came in the mail today. They are the same. No white cover though. I got them at Mouser Electronics
    Mouser p/n 571-3-640433-9 mfg p/n 3-640433-9

  7. #20
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    1,819
    A lot of times it's just the nature of power utility switching, and the control sees a funny cycle while it's running.

    I'm not sure what the dates were for the switch from 100 to the 200/280 panel.
    I know our outfit has a 200 from 1995, and three 200 panels installed as updates in 1998.
    God Bless our Veterans

    God Bless the USA

  8. #21
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,135
    rick


    thanks for thereply. by chance, how many pins on that one?


    r404a

  9. #22
    Join Date
    Feb 2003
    Location
    Wichita Ks
    Posts
    1,457
    9 pins

  10. #23
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,135
    thanks rick

  11. #24
    Join Date
    Jul 2006
    Location
    The Great country of Texas
    Posts
    429
    McQuay monitors the 5.0VDC in case a sensor shorts and drags the voltage down. This would mean none of the sensors or transducers wouls be reading correctly so they initiate a shut down. More that likely, you will have to replace the 280 processor. Good news is you can get a rebuilt but make sure you tell them to load the software you have or it will come empty.
    "I'm from Texas, what country are you from?"

  12. #25
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,135
    good tip, stickerhead. thanks for the input. speaking of programming, if one is sent out not programed, contractors get the software to do it in the field?


    r404a

  13. #26
    Join Date
    Jul 2006
    Location
    The Great country of Texas
    Posts
    429
    Quote Originally Posted by r404a View Post
    good tip, stickerhead. thanks for the input. speaking of programming, if one is sent out not programed, contractors get the software to do it in the field?


    r404a
    Not unless you have Win Monitor software
    "I'm from Texas, what country are you from?"

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event