    high oil temp on a trane rtua

    I am working on a trane rtua 100 chiller and I'm having a problem with high oil temp, my guess is that the txv for the oil cooler is bad? The circuits sub cooling is at 20 deg and superheat is at 9 deg
    Oil temp is gets up to 170 deg. I did check oil level and its ok. Am I missing anything in my troubleshooting?

  2. #2
    Join Date
    Jun 2009
    Location
    Florida
    Posts
    540
    On just one circuit or both? If only one, then how does the oil delta t compare to the other circuit? Are your sc/sh numbers for the oil cooling circuit or the main circuit? How does the filter delta p compare on the two circuits? Are your sensors reading accurately?
    Low Pressure Forever!

    If you know heavy metal, you can work anywhere-Dave Andreson

    Anchors Aweigh my boys, Anchors Aweigh!
    Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!

  3. #3
    Join Date
    Aug 2009
    Posts
    4
    The sh/sc is on the cooling circuit. The problem is only on w circuit (circuit 2) as far as delta t and delta p it is the same except for 2nd circuit is running a much hiher temp.

  4. #4
    Join Date
    Jun 2009
    Location
    Florida
    Posts
    540
    Assuming you have subcooled liquid to the expansion valve of the oil cooler, how cool is the refrigerant outlet of the cooler? How does it compare to the outlet on the other cooler at similar load?
    Low Pressure Forever!

    If you know heavy metal, you can work anywhere-Dave Andreson

    Anchors Aweigh my boys, Anchors Aweigh!
    Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!

  5. #5
    Join Date
    Aug 2009
    Posts
    4
    I did not compare the temp on the two coolers. The one that I'm having the problem with the temp in is at 170 deg and the outlet is at 168. The solinoid is energized for the oil cooler and the temp before the txv is 90 and 170 after.

  6. #6
    Join Date
    Jun 2009
    Location
    Florida
    Posts
    540
    You're too high on both circuits. Normal oil temp is around 130. Also your sh should be 4 deg. Check your charge and EXV operation.

    Make sure your sat. evap and comp suct sensors are accurate and that your drier cores aren't restricted.
    Last edited by ChillerWisperer; 08-24-2009 at 04:56 PM.
    Low Pressure Forever!

    If you know heavy metal, you can work anywhere-Dave Andreson

    Anchors Aweigh my boys, Anchors Aweigh!
    Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!

  7. #7
    Join Date
    Jun 2009
    Location
    Florida
    Posts
    540
    Sorry, I just reread your post and realized the 168/170 was on the same circ. If you're getting 170 on the ref. outlet of the txv, then it's def. closed.
    Low Pressure Forever!

    If you know heavy metal, you can work anywhere-Dave Andreson

    Anchors Aweigh my boys, Anchors Aweigh!
    Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!

  8. #8
    Quote Originally Posted by ChillerWisperer View Post
    Sorry, I just reread your post and realized the 168/170 was on the same circ. If you're getting 170 on the ref. outlet of the txv, then it's def. closed.
    excellent discussion!!! How did this end? What was the reason, for High oil temp?. I'm having same kind of problem here, too.