    Chiller, air condenser,fan blades

    I have a question regarding blade position in shroud, of an air condenser, using 14 fans. On a % basis, should most the blade,be in the shroud ,say, 70%,or only say 30% for max air movement? Some one told me most of the blade should be below for more air movement,but with many fans working to pull the air through I thought maybe Pressure differential, might be more into play then, volume. Does anyone have any thoughts on this?

  2. #2
    Join Date
    Jul 2009
    Posts
    31
    Post Likes
    Thread Starter

    Blade,s

    I notice Trane for this unit, puts the blade hub even with the shaft, which puts the blade mostly (70% to 80%) in the shroud,( I was thinking this might have been done for easier removal of blade,s) I feel we need more air movement,I have allready replaced half flow with full flow blade,s, but was now contemplating, moving the blade,s more into condenser, for greater volume,once again any thoughts?

  3. #3
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Why do you feel that you need to change the unit design by changing the blades or the blade position? What's the original design, and how is the machine operating at present? Blade position is something that is set by the manufacturer according to fan speed, design, orifice design, etc.

  4. #4
    Join Date
    Jul 2009
    Location
    In a mechanical room....
    Posts
    1,908
    Post Likes

    Red face

    Klove is correct and I don't think trane did it to make it easier to remove the blade. If you are having issues such as high head you should take into consideration many parameters such as superheat, sub cooling, chiller approach, ect. If you just want to change the design just bec you feel like it don't! Like klove said they do things for a reason.

  5. #5
    Join Date
    Jul 2009
    Posts
    31
    Post Likes
    Thread Starter
    Well as far as the half flow blades are concerned, the discharged air,was reentering the condenser, If you where standing next to the chiller you could feel it. The half flow fans made it possible to cool at 0 F and the full flow from 15 F, We do not cool under 50 F. On cool days this discharge air returning was not an issue but on very hot days our head would go to high and cause shut down on various things related to high head. AS far as the blade position in the shroud I will just go with what most of the blades where set at , as I try it deeper in and it did not seem to make that much of a difference. As far as questioning how anything works or was done on this machine ,At a latter date I will make a full list of all the things I have found wrong ,bad motor,s broken wiring to fans,leaks ,compressors running out of control because of loading issue,s , fans not staging fast enough etc..... ect.... As far as having a highly trained tech come out , this has been done 2 time every year since I have been here (8 years), things seem to run fine until it got hot out. LOL I may be no expert at this but I am getting things done. We where still running over 107 F on the roof which since I have been here was unheard of.

  6. #6
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Given the problem you are describing, is the coil clean?

    Mess with motors and blades all day long, if the coil isn't clean it won't make a difference.



  7. #7
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    The Trane chillers must have the half pitch blades. The RTAA uses fan staging depending on the saturated condenser and saturated evap temps. The lead fans could need be half pitch.

    Is your UCM set up for either 0 or 15 degree ambient fan configuration? If you are using 0 it will lead with half pitch. 15 leads with full pitch.

    Also check your refrigerant temp sensors. Make sure they are in range. They fail often.
    UA LU189

  8. #8
    Join Date
    Jul 2009
    Posts
    31
    Post Likes
    Thread Starter
    Bring your finest china, they are spotless.

  9. #9
    Join Date
    Jul 2009
    Posts
    31
    Post Likes
    Thread Starter
    The fan staging works great except its about 20 minute to late.I plan on doing the e-prom install before next years heating season, though the comments I have heard on here where not to promising. Anyway besides the staging, the real problems occured when fans where allready at 100% and the discharge air was reentering the condenser. The half flows are off and replaced with full flow so I do not think this will be to much of a problem any more.

  10. #10
    Join Date
    Jul 2009
    Posts
    31
    Post Likes
    Thread Starter
    And yes I set the parameters in the factory menu to D to reflect the fact that half flows where replaced.

  11. #11
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Seems to me, then, that the whole issue could have been avoided by getting rid of the recirced air to the condensers. What is causing this issue, and can it in any way be corrected?

  12. #12
    Join Date
    Jul 2009
    Posts
    31
    Post Likes
    Thread Starter

    Talking

    Thanks all for the input problem is solved. TIM

  13. #13
    Join Date
    Apr 2009
    Location
    In the south
    Posts
    30
    Post Likes
    Sounds to me like you are addressing the wrong issue. You should be looking at what is causing the air to recirculate. What reason is there that the air is not moving away from the unit. You can change the motors but you will still have an air circulation problem. Problem doesn't sound like it is with the machine but more with the installation.

  14. #14
    Join Date
    Jun 2009
    Location
    Southwest Florida
    Posts
    543
    Post Likes
    Quote Originally Posted by klove View Post
    What is causing this issue, and can it in any way be corrected?
    Mr. Gorbachev, tear down that wall!

    Chillers is ugly! Walls are purrrty!
    Low Pressure Forever!

    If you know heavy metal, you can work anywhere-Dave Andreson

    Anchors Aweigh my boys, Anchors Aweigh!
    Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!

  15. #15
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Quote Originally Posted by porttss View Post
    Thanks all for the input problem is solved. TIM
    My personal opinion, Tim, is that if you've got time to give this much of a response, that you owe it to those who offered help (and those that simply view the thread) to let us all in on what the solution is. Everyone on this site needs to benefit from the experiences of others, thus the whole reason for being here. Just to cut everyone off like you're really the only one that counts in the overall scheme of things seems exceedingly ungrateful.............

  16. #16
    Join Date
    Jul 2009
    Posts
    31
    Post Likes
    Thread Starter

    e-prom kits

    Sorry Klove, I just thought it was going in all sorts of directions. Yes building a structure between the chiller,s or on top of the chillers would have solved this problem. Most of the air that was coming back around to the condenser was in the area of the half flow fans, We do not start cooling til after 50 F. The half flows are good til 0 F and the full flows to 15 F but as I stated we do not cool til over 50 F. So just changing these half flows out where the solution in are case. Once again it mostly only happened in the area of the half flows, . And the only time any of this was a problem was over 100 F. It seem from what I am reading about these machines (RTAA-300) is they where good machines they just needed a few extra things ( lip seals , eprom up date,s) 2 compressor,s have had the lip seal problem and 3 more are showing the same problem ,as per symptom causing overloading, as discussed in RTAA-SB-18. I believe it was mainly the 100 tons that had this problem. In my original post I asked where the blade should be on the shaft in the shroud Trane has them mostly in the shrould with only about an inch and a half below. I tried going lowwer but did not feel much of a differance, some have asked why I am doing this and my reply would be to get as much air as I could across the CC. Any way my only question now would be does trane still give these eprom kits for free ? Thanks TIM

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •