Thread: Lightning hit my underground gasline!!!

  1. #1
    Join Date
    Jan 2007
    Posts
    50
    Post Likes

    Lightning hit my underground gasline!!!

    Here's a new one, at least for me:

    I was awakened around 1 a.m. by a sudden, torrential downpour that wasn't even forecast the day before. After just a minute or so -- BANG! -- with no interval between the clap of thunder and the flash of light.

    I was going to roll over and go back to sleep but I decided to get up and see if the power had been knocked out. I discovered 5 of the 10 fuses in my ancient service panel had been blown out, blackened actually, and that the phone was out.

    As I came back up the basement stairs I could smell gas from somewhere -- but not from the furnace or water heater. When I stuck my head out the front door, the rain had stopped but there was a loud gushing, bubbling sound coming from near the gas meter, along with a REAL strong odor of gas. Needless to say, I grabbed cell phone and called the gas company from the other side of the house (upwind). They arrived in 15 minutes, and looking quite alarmed, shut the gas off at the street.

    Later, when they returned to repair the line, they found a charred fitting where the metal pipe from the meter joins the plastic line that comes up from the street. And this line is almost 3 ft. deep!!!

    Question for anyone here: Aren't gas lines supposed to be grounded in order to prevent this kind of thing? What else can one do to protect gas lines and meters from lightning strikes? I always have worried about the phone & electric during storms, unplugging everything I could if a t-storm is forecast. Should I take this up with my gas company or report it to the public service commission?

    Something I never thought would happen. I shudder when I think that the whole house could have blown up.

    AB

  2. #2
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    They do bond them with wire

    The meter bar is supposed to be bonded with a wire that runs with the plastic service to the main. It's also what they locate with a metal detector on plastic mains.

    My guess is that it went into the dirt FROM the meter.

    It can also hit curb boxes above curb cocks and travel up the main from there.

    Noel

  3. #3
    Join Date
    Sep 2005
    Posts
    115
    Post Likes
    I worked as an area engineer with a major gas company for several years, and we've never bonded the meter bar, or anything else for that matter. The tracer wire which is run with plastic service distribution piping normally is just wrapped around the meter riser for storage, but never attached to anything. The light guage wire is designed as a tracer, not as a bonding or ground wire. Lightening strikes to gas meters are normally never a concern, as they typically are located so low to the ground that the lightening is most likely to hit higher protrusions. My former company is gradually relocating all gas meters to be adjacent to the house or building, rather than in the alley or yard. But lighting strikes to gas meters are extremely rare circumstances.

  4. #4
    Join Date
    Oct 2007
    Location
    Austin Texas
    Posts
    2,027
    Post Likes
    I've had lightning take out buried water lines as well. The problem is that sometimes the ground for the building is bonded to the water line coming up from the slab.
    Nemo me impune lacessit.

    How much blood do I have to bathe in to get clean?

    Don't look down on anyone unless you're helping them up.

  5. #5
    Join Date
    May 2000
    Location
    Colorado flatland native
    Posts
    15,068
    Post Likes
    Quote Originally Posted by AlexGB View Post
    . I shudder when I think that the whole house could have blown up.

    AB

    I think you were close. That is why, you'll notice, gas lines break ground before they enter your home, so leaking gas will to. But an open window and correct breeze could blown you to smithereens!
    My doctor gave me six months to live, but when I couldn't pay the bill he gave me six months more.
    Walter Matthau

  6. #6
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,414
    Post Likes
    Lightning is just weird as is all of electricity.

    When I was much younger helpin Dad work on appliances we went into a house that was struck by lightning. There were a couple traces along the wall where the plaster was blown out right where the romex was run. The entertainment center that was plugged into it never had a problem.

    The microwave (why we were there) was toast, but no signs of any major damage inside, no huge burn marks or melted goods. Just didn't work (bad magnetron I believe was the issue).
    "If you call that hard work, a koala’s life would look heroic."

  7. #7
    Join Date
    Apr 2004
    Location
    Muskegon, Mi.
    Posts
    425
    Post Likes
    Around here you have to ground any stainless steel flexible gas lines to a grounding rod with a 6 gauge ground wire.

  8. #8
    Join Date
    Nov 2005
    Location
    Winnipeg MB Canada
    Posts
    438
    Post Likes
    It sounds like you had a curb stop at the street side. Here in my city I can think of only a few streets that have that and they were put in back in the 1960's. And with lack of use they probaby don't work anyway in an emergency!

    Usually the Centra Gas crews try to pinch the exposed line off while waiting for the u/g utility clearences to dig the street up and cap it off at the main.

    I see you said you phone is dead how did the rest of the electronics and appliances make out?

  9. #9
    Join Date
    Jan 2007
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by mbhydro View Post
    It sounds like you had a curb stop at the street side. Here in my city I can think of only a few streets that have that and they were put in back in the 1960's. And with lack of use they probaby don't work anyway in an emergency!

    Usually the Centra Gas crews try to pinch the exposed line off while waiting for the u/g utility clearences to dig the street up and cap it off at the main.

    I see you said you phone is dead how did the rest of the electronics and appliances make out?
    Yeah, this street goes back to the early 50s.

    Since you asked about electronics:

    1) Garage door opener: Circuit board fried. (Probably a good thing, because the garage is adjacent to where most of the escaping gas was drifting -- the spark from the opener might have been a source of ignition) eek 2

    2) Two 48" fluorescent worklights in the basement: Bulbs burnt/blackened and ballasts apparently shot

    3) TV dead. Not a huge loss...a 6-year old tube-type set, and I've been itching for a digital LCD model anyway. :-)

    4) Computer OK but DSL modem and network adapter cooked.

    5) GFIs in kitchen are inop. I tried replacing one myself and circuit was still dead, so time for the electrician.

    6) Last but not least -- my wonderful Rheem RGFD furnace is inop, which is OK this time of year (I don't have a/c). The gas company technician who repaired the line outside identified a small automotive-type fuse that had blown, located on the circuit board inside the blower compartment but when I replaced it the new one promptly blew. Gulp. Any idea of what a new main circuit board for one of these beauties costs?

    I contacted the contractor who installed the furnace and he suggested that I wait until the electrician has checked everything out before he comes out to troubleshoot & repair the furnace. I'm having a modern panel with circuit breakers, better grounding AND a whole-house surge supressor installed. yes1

    Thanks for the replies.

    Alex

  10. #10
    Join Date
    Nov 2008
    Posts
    1,673
    Post Likes
    Some flexible gas lines (yellow colored?) are very thin-walled and there is a class action lawsuit over this. There are also restrictions on how close to other conductors these lines can be placed.

  11. #11
    Join Date
    Aug 2009
    Posts
    31
    Post Likes
    Quote Originally Posted by AlexGB View Post
    Yeah, this street goes back to the early 50s.
    Since you asked about electronics:
    1) Garage door opener: ...
    2) Two 48" fluorescent worklights in the basement: ...
    3) TV dead. ....
    4) Computer OK but DSL modem and network adapter cooked. ...
    Lightning seeks earth ground. Typically, you had damage because a lightning strike even to wires down the street found earth ground via your house. Your damage implies a massive earth ground failure.

    The surge entering your house, apparently, found a path to earth via the gas line. Why did so much energy dissipate on that path? Well, how many feet from the breaker box to an earthing electrode that both meets and exceeds post 1990 National Electrical Code? That is where lightning should have found earth. Apparently you earth ground is that defective - or just as bad, a connection across the basement to a cold water pipe.

    In another situation, the neutral wire in the transformer failed. They also did not have proper earthing. So the electric service had to find earth via the gas line. Eventually that gasket broke down as the meter exploded in the garage. The electric company investigator said that the owners were not home. And that their transformer failure caused the to be at least partly responsible. However, the neutral wire failure would not have caused an explosion if their earth ground existed.

    That would explain your gas line failure. Meanwhile, the surge found earth through many other appliances because you do not have effective protection. Every wire in every cable must connect to earth before entering the building. The neutral wire connects direct. Other two 'hot' AC wires must make that 'less than 10 foot' connection to single point earth ground via a 'whole house' protector. Sounds like you had no 'whole house' protector and woefully insufficient earthing which explains all that damage.

    For example, the DSL modem. Incoming on AC mains and seeking earth ground. All phone lines already have a 'whole house' protector. Therein is another destructive path to earth. Outgoing via the phone line. Since the modem had both an incoming and outgoing path to earth, then the modem was also damaged.

    This is probably the first you have heard of this. And yet what is posted here was long understood before even transistors existed. What was done in high reliability facilities 100 years ago is now required in every home. That means earthing that meets and exceeds post 1990 code. Apparently your home does not even meet 1990 code which explains so much damage.

    A direct lightning strike means nobody even knows the surge existed - if well proven technology is installed. For example, a 'whole house' protector costs about $1 per protected appliance. Only more responsible companies sell these such as General Electric, Square D, Intermatic, Keison, Polyphaser, Leviton, or Siemens. The Cutler-Hammer protector sells in Lowes for less than $50. Only the rare surge causes damage. How often do such surges exist? A question you should never have to answer. Effective protection means you never knew a surge existed. Effective protection (earthing) means even the protector remains functional. A protector is only as effective as its earth ground. Proper earthing means the surge need not find earthing destructively via the furnace and gas line.

  12. #12
    Join Date
    Nov 2008
    Posts
    1,673
    Post Likes
    Quote Originally Posted by westom View Post
    How often do such surges exist?
    See Fig. 8.1 in the link below
    http://books.google.com/books?id=SYh...age&q=&f=false

  13. #13
    Join Date
    Jul 2009
    Location
    Southern Calif.
    Posts
    110
    Post Likes
    We used to have the gas lines bonded and grounded, but found that we had to remove the connections because the small static current was causing electrolysis in the pipe fittings and causing leaks. I’m not an engineer and don’t know the specifics as to how this works. I just know that I was tasked with the job of removing the ground connectors at 15 sites with propane tanks.

    I also know that lighting will always find a weak spot.

  14. #14
    Join Date
    Jan 2007
    Posts
    50
    Post Likes
    Thread Starter
    Wow...informative posts, here. It sounds more and more as though the real problem is with my antique electrical system.

  15. #15
    Join Date
    Feb 2004
    Location
    Connecticut
    Posts
    1,666
    Post Likes
    Quote Originally Posted by mark g View Post
    My former company is gradually relocating all gas meters to be adjacent to the house or building, rather than in the alley or yard.
    WHY? Isn't it ewasier for the meter readers to go up and down an alley and read them than it is to have to go in every single back yard?

  16. #16
    Join Date
    Aug 2009
    Posts
    31
    Post Likes
    Quote Originally Posted by AlexGB View Post
    Wow...informative posts, here. It sounds more and more as though the real problem is with my antique electrical system.
    Implied is a problem that even violates antiquated standards. A problem too often seen in many older homes.

    Too many see lights working. Then assume everything is OK. Classic junk science reasoning. Without inspection, you have little idea (yet) what you have.

  17. #17
    Join Date
    Nov 2008
    Posts
    1,673
    Post Likes
    Quote Originally Posted by AlexGB View Post
    Wow...informative posts, here. It sounds more and more as though the real problem is with my antique electrical system.
    Stress test your elec. system.
    Plugging in a 10A, 120v hair dryer should result in no more than a 3vac drop from the 120vac at that outlet.
    Slapping a 20A load on your 240v supply should drop ~0.4vac from the 240vac, measured at the panel.

  18. #18
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,434
    Post Likes

    Exclamation

    http://www.idealindustries.com/prodD...?prodId=61-165

    Great tool. Can help explain when electronic ignition systems fail, too.

    If you go onto the websites of the various CSST mfrs., you will see specific bonding instructions in light of the class action lawsuit. Note: you are 'bonding'---not 'grounding' the CSST.

    Gas lines cannot be used as a ground but should be bonded if there is a chance they can be energized.

    The electric meter and the distribution panel should be bonded to an grounding electrode conductor. The GEC can be 'ground rods' or other systems such as a Ufer. The water lines and gas line are usually all bonded at a gas WH. Also, it is a good idea to peek at the water meter because sometimes the bonding jumper is left disconnected, which could put you and everyone in the house at risk, esp. if that is intended as the GES.

    HTH,
    Hearthman

  19. #19
    Join Date
    Aug 2009
    Posts
    31
    Post Likes
    Quote Originally Posted by WhoIsThat? View Post
    Stress test your elec. system. ...
    Slapping a 20A load on your 240v supply should drop ~0.4vac from the 240vac, measured at the panel.
    The essential and code required earth ground could be completely missing. And that test would report everything as OK.

    There is only one way to confirm that so critically important earth ground - visual inspection.

    That Ideal tester also reports nothing about the earth ground. It only tests for wire polarity, voltage, and safety ground - not earth ground. Implied was a problem directly traceable to a missing earth ground. That Ideal tester would report everything OK even while the earth ground remained completely missing.

    Appreciate a major difference between the earth ground and safety ground (also called equipment ground). They are not same.

  20. #20
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes
    "GFIs in kitchen are inop." Quote

    Your spike came down neutral on this one, not down hot. Check your neutral grounding, also have utility check neutral to their stepdown transformer.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •