Page 1 of 2 12 LastLast
Results 1 to 13 of 25

Thread: Carrier 30gxn

  1. #1
    Join Date
    Nov 2009
    Posts
    24
    Post Likes

    Carrier 30gxn

    carrier 30gxn 090 chiller - Unit is down with no alarms. Setpoint is set at 45* water temp is 78*. Flow switch is closed. When i turn it off then back on exv's close down but unit will not start. In test mode circuit 'A' will come on. But when i test circuit 'B' it will not. Any ideas why this will take place and why the unit won't run. Thanks

  2. #2
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,843
    Post Likes
    What is the position of the remote- off- enable switch when it doesn't run? And it sounds like maybe circuit B is disabled in the service mode.

  3. #3
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,843
    Post Likes
    Also another thought did you turn service test off?

  4. #4
    Join Date
    Nov 2009
    Posts
    24
    Post Likes
    Thread Starter
    switches are in "emergency on" and "enable" . sevice test is off

  5. #5
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,843
    Post Likes
    Did you check your modes? Check your input for GEN.I , switch and flow.

  6. #6
    Join Date
    Nov 2009
    Posts
    24
    Post Likes
    Thread Starter
    I havent but i will check in the morning

  7. #7
    Join Date
    Nov 2009
    Posts
    24
    Post Likes
    Thread Starter
    i did notice that the red light on the MBB board when it blinks, it doesnt go all the way out

  8. #8
    Join Date
    Dec 2006
    Location
    phoenix
    Posts
    286
    Post Likes
    This could be a few things but I did a similar problem once. The toggle switch was bad. Once I replaced it, the chiller worked fine. I could run components in TEST mode but nothing would run automatically. I had another 30GX chiller exhibit erratic symptoms the following summer, so I replaced both toggle switches and I've never had a recurring problem with it.
    Good Listener has a good point about checking inputs. Good Luck

  9. #9
    Join Date
    Dec 2009
    Location
    Dallas
    Posts
    15
    Post Likes
    You can check under run status to verify switch position. Should show on local when switch is in enable.
    Local 100

  10. #10
    Join Date
    Nov 2009
    Posts
    24
    Post Likes
    Thread Starter
    it does say on local

  11. #11
    Join Date
    Nov 2009
    Posts
    24
    Post Likes
    Thread Starter
    Checked configuration. Looked correct.
    Gen.1 stst - strt
    flow - on
    cnd.f - on

    oil.a and b - closed
    opt2 ctrl - switch

    run status - view - stat - on local
    occ - yes
    mode - no overrides in effect


    checked hps and flow switch just to be sure. This unit should be running but it does nothing
    no alarms at all. last one was flow switch.
    Am I missing something? help sure would be appreciated. thanks

  12. #12
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,843
    Post Likes
    Did you happen to see that the water temps were and what the control setpoint was ? Did someone play around in the configuration or something?

  13. #13
    Join Date
    Dec 2009
    Location
    Dallas
    Posts
    15
    Post Likes
    You have full model #? what controls on the chiller?