    Trane RTAC 200 - Noise expectations

    I am looking for a typical dB rating for this chiller. I have been unable to find anything being published from Trane.

    Thank you,

  2. #2
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,086
    I dont know about the Db ratings but I wouldnt install one in a noise sensitive area without the sound blanket option . They are a PITA for service but make a huge noise difference . Also follow the installation guidlines . "NO BRAIDED PIPING ISOLATERS" and dont hang the piping on the chiller frame .
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  3. #3
    Join Date
    Nov 2008
    Posts
    366
    That can be found in the submittal data provided by the Trane New System Salesman.

  4. #4
    Join Date
    Mar 2005
    Location
    Indiana
    Posts
    159
    Don't know the db rating but keep in mind that a remote evp is much more noisy than a package unit. Haven't found the solution for that yet, it seems to be a harmonic problem.

  5. #5
    Join Date
    Aug 2009
    Location
    Scranton Pa
    Posts
    24
    I actually have a submittal at my office for that exact machine with the ratings. They're no louder than any other 200 ton air cooled screw screamer. I can scan it in and post it tomorrow morning. Its rejected BTW lol. Not because of the sound, because it doesn't operate as well as a Carrier 30XA with variable primary and required an additional 200 amps of breaker capacity.

    If you need an air cooled machine, and it is a sound sensitive scenario, definitly use the blankets and low sound fans, but look into a barrier, as provided by AcoustiBlok or Kinetics.

  6. #6
    Join Date
    Aug 2009
    Location
    Scranton Pa
    Posts
    24

    RTAC Sound Pressure

    Boston,

    See attached for equipment sound power. You'll have to convert it to sound pressure based on the distance from the machine.
    Attached Files Attached Files

  7. #7
    Join Date
    Jul 2008
    Location
    Greater Boston Area
    Posts
    8

    Thumbs up Thank you for all of your input.

    Thanks again.

  8. #8
    Join Date
    Nov 2006
    Location
    North Carolina
    Posts
    130
    Quote Originally Posted by FlewtheCoop View Post
    I actually have a submittal at my office for that exact machine with the ratings. They're no louder than any other 200 ton air cooled screw screamer. I can scan it in and post it tomorrow morning. Its rejected BTW lol. Not because of the sound, because it doesn't operate as well as a Carrier 30XA with variable primary and required an additional 200 amps of breaker capacity.

    If you need an air cooled machine, and it is a sound sensitive scenario, definitly use the blankets and low sound fans, but look into a barrier, as provided by AcoustiBlok or Kinetics.


    The York YCIV is a whole lot less noisy than the Trane RTAC. Have several of each under contract.

  9. #9
    Join Date
    Jun 2007
    Location
    Here. I'm right here i tell you!
    Posts
    465
    Quote Originally Posted by chad_nc View Post
    The York YCIV is a whole lot less noisy than the Trane RTAC. Have several of each under contract.
    Its even less noisy when silent night mode is active. Of course you can only get up to about 60 percent in that mode before it reverts back to the normal operating mode.