Results 1 to 9 of 9
08-19-2009, 04:09 PM #1
- Jul 2008
- Greater Boston Area
- 8
Trane RTAC 200 - Noise expectations
I am looking for a typical dB rating for this chiller. I have been unable to find anything being published from Trane.
Thank you,
08-19-2009, 05:26 PM #2
I dont know about the Db ratings but I wouldnt install one in a noise sensitive area without the sound blanket option . They are a PITA for service but make a huge noise difference . Also follow the installation guidlines . "NO BRAIDED PIPING ISOLATERS" and dont hang the piping on the chiller frame .
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!
08-19-2009, 08:27 PM #3
That can be found in the submittal data provided by the Trane New System Salesman.
08-19-2009, 09:12 PM #4
- Mar 2005
- Indiana
- 125
Don't know the db rating but keep in mind that a remote evp is much more noisy than a package unit. Haven't found the solution for that yet, it seems to be a harmonic problem.
08-19-2009, 10:06 PM #5
I actually have a submittal at my office for that exact machine with the ratings. They're no louder than any other 200 ton air cooled screw screamer. I can scan it in and post it tomorrow morning. Its rejected BTW lol. Not because of the sound, because it doesn't operate as well as a Carrier 30XA with variable primary and required an additional 200 amps of breaker capacity.
If you need an air cooled machine, and it is a sound sensitive scenario, definitly use the blankets and low sound fans, but look into a barrier, as provided by AcoustiBlok or Kinetics.
08-20-2009, 06:47 AM #6
RTAC Sound Pressure
Boston,
See attached for equipment sound power. You'll have to convert it to sound pressure based on the distance from the machine.
08-20-2009, 08:54 AM #7
- Jul 2008
- 8
Thank you for all of your input.
Thanks again.
08-23-2009, 10:17 PM #8
- Nov 2006
- North Carolina
- 125
09-06-2009, 10:24 PM #9