    Heya all,
    How do you assign / unassign a MP580 on the BCU?
    Do I need to do this through Rover or can it be done through the summit software? How

  2. #2
    Join Date
    Oct 2003
    Location
    Hanging out in the brewhouse
    Posts
    820
    Post Likes
    It is done through Tracer Summit.
    Setup.....Site Configuration.....Devices.....Assign Neuron ID button.
    Beware of the prophet trying to make a profit.

    There is less oxygen from knee level to the floor! Check it out next time you tie your boots.

  3. #3
    Join Date
    May 2009
    Location
    Michigan
    Posts
    62
    Post Likes
    Thread Starter

    qtip

    when I went to do this the following occured:
    Error Type Network Variable
    Critical Link Error -421

  4. #4
    Join Date
    Oct 2003
    Location
    Hanging out in the brewhouse
    Posts
    820
    Post Likes
    Sounds like you are going to lose some more hair!!!!!

    Can't help you out....never seen that before!!

    Good Luck
    Beware of the prophet trying to make a profit.

    There is less oxygen from knee level to the floor! Check it out next time you tie your boots.

  5. #5
    Join Date
    Jun 2004
    Posts
    833
    Post Likes
    At which point did it throw the error code. When you clicked assign neuron id? or sometime after?

  6. #6
    Join Date
    May 2009
    Location
    Michigan
    Posts
    62
    Post Likes
    Thread Starter

    error code

    went to error code after it tried to discover.
    Now I have 6 devices that do not have neuron id s
    so everything is popping up question marks.
    Question, if your comm wire is not hooked up will it still give you a neuron id?

  7. #7
    Join Date
    Apr 2008
    Location
    Nevada
    Posts
    58
    Post Likes
    Quote Originally Posted by bellemech View Post
    went to error code after it tried to discover.
    Now I have 6 devices that do not have neuron id s
    so everything is popping up question marks.
    Question, if your comm wire is not hooked up will it still give you a neuron id?
    No, Tracer will not discover Neuron IDs with the cable disconnected. It will only display Neuron IDs in the database.

    Do you have more or less UCM's created than neurons on the link?

    Are any devices offline that are in the database when you did your discovery?

    Have any new devices been added to the link?

    If old devices are in the database but are offline have they been permanently removed?

    You may have to rebuild the link to cure this problem. Before you take such invasive action you should determine if there are any custom bindings between devices on the link, be sure that all the controllers on the link are online, and that the number of UCMs matches the number of neurons on the link.
    The bindings will be wiped out in the process and will need to be recreated with Rover.
    Offline controllers will be removed from the data base.
    Tracer will complain if the number of UCMs doesn't match the number of neurons.
    If new devices have been added you will need to created a UCM for them and assign the discovered neuron ID to it.

    Regards,
    Boardsmoker

  8. #8
    Join Date
    Apr 2008
    Location
    Nevada
    Posts
    58
    Post Likes
    Quote Originally Posted by bellemech View Post
    went to error code after it tried to discover.
    Now I have 6 devices that do not have neuron id s
    so everything is popping up question marks.
    Question, if your comm wire is not hooked up will it still give you a neuron id?
    No, Tracer will not discover Neuron IDs with the cable disconnected. It will only display Neuron IDs in the database.

    Do you have more or less UCM's created than neurons on the link?

    Are any devices offline that are in the database when you did your discovery?

    Have any new devices been added to the link?

    If old devices are in the database but are offline have they been permanently removed?

    You may have to rebuild the link to cure this problem. Before you take such invasive action you should determine if there are any custom bindings between devices on the link, be sure that all the controllers on the link are online, and that the number of UCMs matches the number of neurons on the link.
    The bindings will be wiped out in the process and will need to be recreated with Rover.
    Offline controllers will be removed from the data base.
    Tracer will complain if the number of UCMs doesn't match the number of neurons.
    If new devices have been added you will need to created a UCM for it and assign the discovered neuron ID to it.

    Regards,
    Boardsmoker

  9. #9
    Join Date
    Apr 2008
    Location
    Nevada
    Posts
    58
    Post Likes

    Exclamation

    oops

  10. #10
    Join Date
    May 2009
    Location
    Michigan
    Posts
    62
    Post Likes
    Thread Starter

    LonTalk Status ??????????????

    Went to assign a neuron id, and the LonTalk Status "Phase 1 Discovery in Progress" Froze.
    Anyone no what is going on?
    Hooked up Rover and it is picking up all of the devices there are "9" on the link.
    The EOL resistor looks good, measures 105k ohms.
    WTF cant get my head around it?

  11. #11
    Join Date
    Feb 2005
    Posts
    293
    Post Likes
    The first thing to try is do a Clear Ram and Reset. This will reset the peak (LONtalk) database in the BCU. Then try the discovery again. Most of the time this take care of it.
    Anyone who says this trade is easy, aint doing it right!

    If you want to hear God laugh, tell him your plans.

    Proud member of the United Association.

  12. #12
    Join Date
    Feb 2005
    Location
    Where it's dark & damp
    Posts
    617
    Post Likes
    Quote Originally Posted by bellemech View Post
    The EOL resistor looks good, measures 105k ohms.
    WTF cant get my head around it?

    End of the line resistor is not good. There should be two so the link resistance should be in the 50 to 60 range. I'll assue the Kilo ohms in your reading is a mistake.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •