+ Reply to Thread
Results 1 to 8 of 8

Thread: Trane RTWA

  1. #1
    Join Date
    Nov 2008
    Location
    Upstate South Carolina
    Posts
    39
    Post Likes

    Trane RTWA

    I'm having a low evap refrigerant temp fault every once in a while, this chiller runs at 28 degrees, its in a lead, lag setup with another chiller,only one circuit runs at a time,(balanced run time is enabled), they switch chiller lead once a week. The fault is on the b circuit, maybe once every 2 months.
    the low temp setting is 2. I checked the slide valve operation and everything seems to work fine, exv is working properly, I increased the exv response time after the first visit but that didnt help, just wondering if anyone else may have had this problem in the past?

    Thanks for any advice.

  2. #2
    Join Date
    Apr 2009
    Location
    In the south
    Posts
    30
    Post Likes
    Check your sensors for proper readings. Also check them for any reading to ground with a digital meter. If there is any reading to ground they should be changed. This can cause periodic trips.

  3. #3
    Join Date
    Aug 2009
    Location
    Scranton Pa
    Posts
    24
    Post Likes
    Its an ice machine I'm guessing? Is it a factory ice controller? Check if there's an "ice done" (that's Carrier terminology, i don't know what Trane calls it) contact and its fully functional. It could be just being forced to run when there's not enough charge required on the tanks.

  4. #4
    Join Date
    Jan 2008
    Location
    Phoenix Arizona
    Posts
    1,663
    Post Likes
    If its not an ice machine check pressure drop across the evap barrel and make sure you have flow...I would check the approach also...
    "If history repeats itself I am so getting a dinosaur"

  5. #5
    Join Date
    Nov 2008
    Location
    Upstate South Carolina
    Posts
    39
    Post Likes
    Thread Starter
    The approach temp on this circuit is about the same as the other circuit, and the other chiller, it runs about 9, its not a ice machine , the other circuit never tripps out, wondering if the slide valve could be sticking intermittedly?
    Thanks for the input.

  6. #6
    Join Date
    Nov 2006
    Location
    North Carolina
    Posts
    136
    Post Likes
    I have had this problem before. What I found was there were two airhandlers on this system, a large and a small. The small runs 24/7 and the large runs 6am-9pm mon-fri. When the large ahu shut down there was not enough load on the machine and it would not unload fast enough and trip off on low evap temp. It did this mainly in colder weather 50-60 deg F. What I had to do to correct the problem was shut the chiller down the same time Large AHU shut down and then turn it back on 15 minutes later. I haven't had the alarm since. The machine just wouldn't unload fast enough and that was the cheapest easiest fix there was. Basically what it came down to was the system did not have enough water in the loop. This may not be your problem but worth a check. Hope this helps


    Chad

  7. #7
    Join Date
    Jan 2008
    Location
    Phoenix Arizona
    Posts
    1,663
    Post Likes
    This might be fixed already but i'm wondering if the machine is designed to run at 28 degrees? or it is running at 28 degrees...Also is 9 degree approach on the evap or condenser side? I would be worried about flow in the evap and pressure drop through the barrel if its evap approach...

    I had a rthc last week that since startup wasn't working right...It turned out instead of a pressure reducing station they used a regulator and took out the adjustment screw...suction pressure was 35# and the expansion tank was full to the top...Also they had the valve on the inlet to the evap barrel closed to deal with the higher pressure and it caused the machine to run really low evap temperature...we drained the loop, replace the regulator and valved off the outlet valve and the pressure drop and ewt/lwt as well as the evap ref. temp were right where they should be...

    The issue with the above problem was it was washing the oil out of the separator and tripping on oil loss...but it was related to the machine basically freezing up...
    "If history repeats itself I am so getting a dinosaur"

  8. #8
    Join Date
    Nov 2008
    Location
    Upstate South Carolina
    Posts
    39
    Post Likes
    Thread Starter
    I changed the sensors and no more faults yet,
    Thanks for the input.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •