Sampling static pressure
Does anyone have a good diagram or easy explaination on where to take static pressure readings on an RTU? The question is geared toward the return side....is your TSP referencing before or after the draw through coil?
BDP 588ANW060100
http://www.docs.hvacpartners.com/idc...i588a-18-9.pdf
http://www.docs.hvacpartners.com/idc...588a.18.4b.pdf
-
08-14-2009, 12:51 PM #2
The blower performance chart is using External Static Pressure (see pg. 41 of your first link).
I would punch wholes in the duct next to the unit if it's a horizontal discharge.
If it's vertical discharge, I'd punch wholes in the horizontal duct connection panels.
If you wanted to use the wet coil pressure drop table on page 44, you'd punch holes in the blower access door and the return panel/duct.Merry Christmas

-
08-14-2009, 09:58 PM #3
Total Static Pressure is fan discharge static-fan suction static.
External Static Pressure is supply static-return static
If the fan discharge static is 2" w.c and the fan suction static is -1", the fan's TSP would be 3" (2"-(-1")
-
08-15-2009, 04:00 AM #4
Regular Guest
- Join Date
- Feb 2009
- Location
- CA
- Posts
- 4
thanks!
-
08-15-2009, 02:05 PM #5
-
08-15-2009, 05:04 PM #6
Glad I could be of assistance.
-
08-17-2009, 12:22 PM #7
Regular Guest
- Join Date
- Jun 2009
- Posts
- 146
-
08-17-2009, 01:16 PM #8
thanks for the diagram
THE MORE I LEARN
THE MORE I FIND I DONT KNOW
Cancer Survivor
And Dam Well
Plan On Staying That Way
-
08-18-2009, 11:19 PM #9
Static Pressure (Sp) This is pressure that is exerted in all directions of a duct. When static pressure = total pressure there would be no flow.
Velocity Pressure (Vp) The difference between total pressure and static pressure.
Total Pressure = Static Pressure + Velocity Pressure.
-
02-08-2010, 09:30 AM #10
Regular Guest
- Join Date
- Jul 2009
- Posts
- 25
Good diagram can somone also diagram this for an AHU with a SF and a RF
-
02-08-2010, 08:04 PM #11

I modified it a bit to show a little more detail and now it has a supply and return fan.Last edited by Tech Rob; 02-08-2010 at 08:46 PM.
-
02-09-2010, 06:59 AM #12
Regular Guest
- Join Date
- Jul 2009
- Posts
- 25
Ext SP
Thanks for the new diagram with the SF and RF. Thats about what I figured. But the reason I wasn't sure is becuase on the Fan shcedule ( on the plans) it has a design ESP for each fan. ( SF & RF ) while I would expect to see a design TP for each fan I thought I would only see one ESP for the AHU not the way they have it...so i'm still a lil confused...but thank you for confirming what I thought...Noel
-
02-09-2010, 06:01 PM #13