  1. #14
    Join Date
    Feb 2016
    Posts
    1
    Post Likes

    Hmm Hot Water Generator taking heat from my Hot Water Tank?

    Hello

    I live in Ontario Canada. (hopefully that's a good start to my thread HA HA)

    I researched on this forum about HWG (hot water generators) and the proper plumbing into a single electric hot water tank.

    I purchased a 10 year old home with a 2005 model Climate Master GSV 060 (5 ton) geothermal unit with HWG. I have owned the home for 2 months and noticed a SUBSTANTIAL amount of electricity consumption. Last month (30 days) 3528 Kw/h. Yep, in Ontario Canada $0.21 per Kw (tax included) equates to $740.00 for the 30 day period. Yeah WOW.

    So, we have no gas what so ever in our area. Geothermal Closed Loop system. Yesterday I conducted an experiment to shut down my hot water tank for 6 hours. It is a 80 Gallon REHEEM unit. I have no bunker (secondary tank). My energy consumption dropped in 1/2 for this period compared to the last 60 days. Here is my concern, I think my HWG is plumbed incorrectly to the HWT. I wanted to enter a picture but cannot figure out how so I will try to explain it. Two lines run from the HWG. (in / out). These two orange lines run into a four way T on the bottom of the tank. One is a drain, the other goes into the tank. Does this not create a vacuum drawing the pre-heated hot water from the tank back into the HWG of the geothermal unit?

    Another little note: on the hot output (on top of the tank) is a circulation pump which circulates the hot water throughout the large home to acquire on demand hot water at the faucets. It's 1/25 HP less than 25W.

    Any specialists that can help me on this would be VERY appreciated. I was told I cannot just close the valves on the bottom of the tank because the HWG pump needs constant circulation. Although, could I just disable the HWG pump and then turn off the valves if in fact this is why all my energy is being drawn from the Hot Water Tank?

    Please help!

  2. #15
    Join Date
    Jun 2013
    Location
    NORTHERN
    Posts
    1,122
    Post Likes
    these aforementioned 4-way T's for recirc in HW tank drain ports, - in one port have fowled in nearly every one of seen installed since the 1980's.

    The PEX tube installers' flood-baths in folks homes are less pretty than where plugged at the 4-way.
    Process cooling: NO COMPRESSORS Earth-Coupled since 1996
    ... however, much still needs to be hybridized energy transfer.

    CLOSED LOOP 2015 listed EER's
    even 49+ now; and "blended from low to high variable speeds" for 32deg.F ~ E-Star

    Perhaps you need a 32F Chiller/HW-Heat: buy a GEO-T Heat Pump (GHP with Heat-Recovery)
    http://www.energystar.gov/index.cfm?...mal_heat_pumps

    http://www.hydro-temp.com/products.html and Bosch/Carrier and AquasystemsInc.com

  3. #16
    Join Date
    Jun 2013
    Location
    NORTHERN
    Posts
    1,122
    Post Likes
    PEX has not held up to the convected HW able to hit 170f RARELY when a circ pump is off and a GHP desuperheater is below a cold fluid in a tank, forcing slow , sometimes over-heated pressurized hot water to pop-off the PEX at the inlet to the GHP ( reversed heat migration, likely during restricted air flow/ blower-failing to wipe off heat/ etc).
    Process cooling: NO COMPRESSORS Earth-Coupled since 1996
    ... however, much still needs to be hybridized energy transfer.

    CLOSED LOOP 2015 listed EER's
    even 49+ now; and "blended from low to high variable speeds" for 32deg.F ~ E-Star

    Perhaps you need a 32F Chiller/HW-Heat: buy a GEO-T Heat Pump (GHP with Heat-Recovery)
    http://www.energystar.gov/index.cfm?...mal_heat_pumps

    http://www.hydro-temp.com/products.html and Bosch/Carrier and AquasystemsInc.com