Thread: charging liquid

  1. #1
    Join Date
    Dec 2006
    Location
    Henryville IN
    Posts
    248

    charging liquid

    Trane RTAA 200ton just short of charge 50 lbs. I charged in vapor just like the manual says. Used heat gun to boost pressure on the tank,but still slow. Now the question, can I trickle in liquid without doing damage to the screw compressor? I did fix the leak, the relief valve blew because of 3 fan failures.

  2. #2
    Join Date
    Mar 2005
    Location
    Indiana
    Posts
    159
    The factory charge on those units are wrong. If you weighed the charge and are 50 lbs shy of the nameplate you should be good. Those units operate the best when sucooling is 15 degrees.

  3. #3
    Join Date
    Dec 2003
    Location
    45th Parallel
    Posts
    954
    You should have a service valve at the outlet of EXV, or inlet to evap. Feel free to dump liquid in there as fast as you like.

    You can charge liquid at the suction service valve also, using common sense. Don't hook up a 125# cylinder with a 3/8 hose and run full open.
    Although it may take it, I wouldn't try it.

  4. #4
    Join Date
    Dec 2006
    Location
    Henryville IN
    Posts
    248
    Quote Originally Posted by drivewizard View Post
    You should have a service valve at the outlet of EXV, or inlet to evap. Feel free to dump liquid in there as fast as you like.

    You can charge liquid at the suction service valve also, using common sense. Don't hook up a 125# cylinder with a 3/8 hose and run full open.
    Although it may take it, I wouldn't try it.
    I was going to charge at the valves after the exv but they were so rusted that I figured I'd be asking for trouble if I'd even touch them with a wrench. I just vapor charged since I had two other chillers down. Thanks for the info.

  5. #5
    Join Date
    Oct 2004
    Location
    Metro ATL
    Posts
    454
    Quote Originally Posted by always looking View Post
    The factory charge on those units are wrong. If you weighed the charge and are 50 lbs shy of the nameplate you should be good. Those units operate the best when sucooling is 15 degrees.
    I don't remember the 200 being a problem. I thought it was only 240 and up and only mfg before June '96. In those cases the second circuit was 100tons and the charge should be 130lbs R-22. Nameplate said 180lbs.

  6. #6
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,440
    Quote Originally Posted by drivewizard View Post
    You should have a service valve at the outlet of EXV, or inlet to evap. Feel free to dump liquid in there as fast as you like.

    You can charge liquid at the suction service valve also, using common sense. Don't hook up a 125# cylinder with a 3/8 hose and run full open.
    Although it may take it, I wouldn't try it.
    if you pull the cores out it will go faster...they can take it easy.
    How to make the perfect "Half-Hitch" knot or any other boyscout knot in 3 easy steps...

    1. Remove your meter leads from the meter and very carefully return them to their storage case or bag.
    2. Wait 2 seconds
    3. Very carefully remove your meter leads from their storage place and enjoy your new knot!

  7. #7
    Join Date
    Oct 2006
    Location
    Central Texas
    Posts
    638
    Quote Originally Posted by blewbyu2 View Post
    I was going to charge at the valves after the exv but they were so rusted that I figured I'd be asking for trouble if I'd even touch them with a wrench. I just vapor charged since I had two other chillers down. Thanks for the info.
    Back up wrenches come in handy there, I'd be careful charging there easy overcharge, as long as you don't do what DriveWizard said you'll be alright.
    Sic Semper Tyrannis.

  8. #8
    Join Date
    Jul 2009
    Location
    In a mechanical room....
    Posts
    1,888

    Hmm

    When ever a unit is large enough and I don't want to load liquid I break out the recovery machine and pull vapor out of the jug and into the unit makes charging much faster! Or you could use cap tube charger eh they suck!

  9. #9
    Join Date
    Jun 2009
    Location
    Florida
    Posts
    540
    Quote Originally Posted by chrishvacman View Post
    When ever a unit is large enough and I don't want to load liquid I break out the recovery machine and pull vapor out of the jug and into the unit makes charging much faster! Or you could use cap tube charger eh they suck!
    Try that on an RTAA and you'll be there a week. Would work well on resi and small commercial...completely different animal.
    Low Pressure Forever!

    If you know heavy metal, you can work anywhere-Dave Andreson

    Anchors Aweigh my boys, Anchors Aweigh!
    Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!

  10. #10
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,596
    Quote Originally Posted by chrishvacman View Post
    When ever a unit is large enough and I don't want to load liquid I break out the recovery machine and pull vapor out of the jug and into the unit makes charging much faster! Or you could use cap tube charger eh they suck!
    assuming we are talking about a large unit, why pump vapor? why not pump in liquid? pumps much faster.

  11. #11
    Join Date
    Jul 2009
    Location
    In a mechanical room....
    Posts
    1,888

    Hmm

    Do you know what happends when you dump liquid refrigerant into a chiller barrel that has a vac? OUCH! So the first 30-50psi better be vapor.

  12. #12
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,723
    Does a recovery machine condense vapor into liquid?
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  13. #13
    Join Date
    Jul 2009
    Location
    In a mechanical room....
    Posts
    1,888

    Thumbs up

    It depends on how much refrigerant you are moving normally no, recovery machine will knock if it's valves are open all of the way if you start to move liquid. The recovery machine pulls vapor from the top of the recovery cylinder and puts it back into the chiller. Think push pull without the pull.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event