charging liquid
Trane RTAA 200ton just short of charge 50 lbs. I charged in vapor just like the manual says. Used heat gun to boost pressure on the tank,but still slow. Now the question, can I trickle in liquid without doing damage to the screw compressor? I did fix the leak, the relief valve blew because of 3 fan failures.
-
08-10-2009, 09:53 PM #2
Professional Member
- Join Date
- Mar 2005
- Location
- Indiana
- Posts
- 126
The factory charge on those units are wrong. If you weighed the charge and are 50 lbs shy of the nameplate you should be good. Those units operate the best when sucooling is 15 degrees.
-
08-10-2009, 10:11 PM #3
You should have a service valve at the outlet of EXV, or inlet to evap. Feel free to dump liquid in there as fast as you like.
You can charge liquid at the suction service valve also, using common sense. Don't hook up a 125# cylinder with a 3/8 hose and run full open.
Although it may take it, I wouldn't try it.
-
08-11-2009, 07:24 AM #4
Professional Member
- Join Date
- Dec 2006
- Location
- Henryville IN
- Posts
- 248
-
08-11-2009, 07:14 PM #5
-
08-11-2009, 07:16 PM #6
-
08-11-2009, 09:19 PM #7
-
08-22-2009, 01:23 PM #8
When ever a unit is large enough and I don't want to load liquid I break out the recovery machine and pull vapor out of the jug and into the unit makes charging much faster! Or you could use cap tube charger eh they suck!
-
08-22-2009, 01:49 PM #9Low Pressure Forever!
If you know heavy metal, you can work anywhere-Dave Andreson
Anchors Aweigh my boys, Anchors Aweigh!
Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!
-
08-22-2009, 02:18 PM #10
-
08-22-2009, 06:32 PM #11
Do you know what happends when you dump liquid refrigerant into a chiller barrel that has a vac? OUCH! So the first 30-50psi better be vapor.
-
08-22-2009, 06:51 PM #12
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,511
Does a recovery machine condense vapor into liquid?
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
08-22-2009, 07:03 PM #13
It depends on how much refrigerant you are moving normally no, recovery machine will knock if it's valves are open all of the way if you start to move liquid. The recovery machine pulls vapor from the top of the recovery cylinder and puts it back into the chiller. Think push pull without the pull.