Trane RTAA 200ton just short of charge 50 lbs. I charged in vapor just like the manual says. Used heat gun to boost pressure on the tank,but still slow. Now the question, can I trickle in liquid without doing damage to the screw compressor? I did fix the leak, the relief valve blew because of 3 fan failures.
-
08-10-2009, 09:53 PM #2
Professional Member
- Join Date
- Mar 2005
- Location
- Indiana
- Posts
- 125
The factory charge on those units are wrong. If you weighed the charge and are 50 lbs shy of the nameplate you should be good. Those units operate the best when sucooling is 15 degrees.
-
08-10-2009, 10:11 PM #3
You should have a service valve at the outlet of EXV, or inlet to evap. Feel free to dump liquid in there as fast as you like.
You can charge liquid at the suction service valve also, using common sense. Don't hook up a 125# cylinder with a 3/8 hose and run full open.
Although it may take it, I wouldn't try it.
-
08-11-2009, 07:24 AM #4
Professional Member
- Join Date
- Dec 2006
- Location
- Henryville IN
- Posts
- 248
-
08-11-2009, 09:19 PM #5
-
08-22-2009, 01:23 PM #6
When ever a unit is large enough and I don't want to load liquid I break out the recovery machine and pull vapor out of the jug and into the unit makes charging much faster! Or you could use cap tube charger eh they suck!
-