On the Rheem RGRL, does the blower speed change with each stage as well as the btu or is it only the btu? I have medium low (yellow) on heat and low (red) on fan.
On first stage, will it run the blower on low or does it run both on the medium low and just the btu goes up?
-
07-20-2009, 03:17 PM #2
On 1st stage, it blows on fan speed. When 2nd stage calls and fire cranks up, it switches to heat speed.
-
07-20-2009, 03:29 PM #3
Regular Guest
- Join Date
- Feb 2007
- Posts
- 997
The furnace has a 2 stage gas valve, which operates at 70% and 100% input. The speed of the blower will change from a lower (first stage) to a higher (2nd stage) speed.
From your post, do I take it that the furnace is already installed? You don't want to be adjusting blower speeds without the requisite knowledge and equipment.
Whether it is low, medium low, medium, etc., is dependent on your duct system and will be adjusted by the contractor during installation, so that the unit's temperature rise (difference in temperature of return and supply air) is in specification for each stage. He may also set the fan's 'on' speed.
I tried to view the mfg's specs, but were unable to retrieve them for better information.
Amp
-
07-20-2009, 03:38 PM #4
Regular Guest
- Join Date
- Jun 2009
- Posts
- 146
Thanks guys. I'm going to have my contractor come out before heating season to make sure the blower settings are appropriate.
-
07-20-2009, 04:07 PM #5
Regular Guest
- Join Date
- Jun 2009
- Posts
- 146
One more question... my contractor refers to my furnace as a 4 ton. Does he mean that it has the capability of moving 4 tons of air, i.e., 1600 cfm?
When I look at the spec document, it actually shows it can deliver up to 2100 cfm on the high blower speed, so wouldn't it really be capable of 5 tons of blowing?
-
07-20-2009, 06:08 PM #6
Regular Guest
- Join Date
- May 2009
- Posts
- 6
The furnace is capable of being matched up to a 5ton AC unit that would need about 2100CFM, but it sounds like your AC and duct system is a 4ton that needs about 1600 CFM.
-
07-20-2009, 06:40 PM #7
Regular Guest
- Join Date
- Jun 2009
- Posts
- 146
Actually, my condenser is a 3 ton. The blower setting is currently on med-low and producing around 1255 - 1490 CFM (depending on static pressure). I don't think my contractor ever measured the actual static, but he initially left the factory settings with blower on high for cool which was producing between 1745 - 2100 CFM. Needless to say, it was VERY noisy before it was changed it to med-low.
Incidentally, my inside coil is a 4 ton.
-
07-20-2009, 08:45 PM #8
I bet 95% of the furnaces installed are left on high from the factory even though low or medium low is appropriate!