    Lots of swampers in west and southwest Texas. People there don't want refer, they are happy with the evap coolers. Always wondered about the water thats being used especially since it's not in endless supply anymore.
    I'm not tolerating Political Correctness anymore, from now on it's tell it like it is.

    Veto Pro Pak - The best tool bag you'll ever own






  2. #22
    Join Date
    Jul 2004
    Posts
    31
    Post Likes
    A rather unsatisfying discussion. Similar to what I'm finding as far as trying to find a good swamp cooler contractor.

    I think evap cooling is being treated as the "bastard stepchild" of the HVAC industry because there's too much maintenance and homeowner involvement required. If the average H.O. paid to have it done correctly (unlikely) the maintenance costs would equal his energy savings.

    Those of us who spend about 4hrs/year fiddling with them ourselves couldn't be happier (.in Denver's climate anyway). Unfortunately, the 4 hrs. would have to be spread to about 6 service calls from a pro.

    It costs me $20/month to cool a house that would run $160 with conventional A/C. The cooling season is roughly 4 months. Two more keys to cooler happiness: 1. Overcool your house at night, 2. Never run the swampie if the ambient temperature gets above about 80*.

    Nowadays, to a professional couple who paid $500,000 to $1.5M for their house, this much involvement is unacceptable.

    (Note to Garya505: Pollen gets scrubbed from the air that passes thru a cooler. I have seen a little mold on the inside of cooler occasionally, however.)

    So here's my question - Does anyone make a controller that can run these things correctly?
    Last edited by kevin_in_denver; 09-03-2009 at 04:42 PM. Reason: add note to Gary

  3. #23
    Join Date
    Aug 2009
    Location
    Seabeck, Wa.
    Posts
    55
    Post Likes
    I've only got one I'm responsible for. It's the make-up air for a big kitchen hood. The summertime rooftop RH here in the Pacific Northwest is pretty low so it's very effective in cooling the air. When I got it working and turned on the water, the cooks thought I had rerouted some AC. It's a pretty old unit that looks like it's had a lot of use. Only thing I'm worried about is remembering to isolate and drain the water line before freezing weather gets here. Didn't see any mold but it had set dry for quite awhile.

  4. #24
    Join Date
    Jul 2004
    Posts
    31
    Post Likes
    Commercial kitchen makeup air is often passed through a swamp cooler, even in humid environments. Better than nothing, since conventional AC is impractical for that much air volume.

    If Evaporative Cooling (EC) replaced AC in all the cities and towns where it works well, this country would literally never need to build a new power plant. That's because all of our plants are severely underutilized except for a couple weeks in the height of summer when AC units are running full tilt. EC where effective would shave that peak demand, and brownouts would cease until we get enough photovoltaic and wind generation capacity installed. Then we can start decomissioning the coal plants, and voila, EC has solved global warming!

  5. #25
    Join Date
    Mar 2008
    Location
    Indy
    Posts
    378
    Post Likes
    Quote Originally Posted by kevin_in_denver View Post
    Commercial kitchen makeup air is often passed through a swamp cooler, even in humid environments. Better than nothing, since conventional AC is impractical for that much air volume.

    If Evaporative Cooling (EC) replaced AC in all the cities and towns where it works well, this country would literally never need to build a new power plant. That's because all of our plants are severely underutilized except for a couple weeks in the height of summer when AC units are running full tilt. EC where effective would shave that peak demand, and brownouts would cease until we get enough photovoltaic and wind generation capacity installed. Then we can start decomissioning the coal plants, and voila, EC has solved global warming!
    Sounds too good to be true. Where can I find this data?

  6. #26
    Join Date
    Jun 2009
    Location
    Southwest Florida
    Posts
    543
    Post Likes
    Quote Originally Posted by kevin_in_denver View Post
    Commercial kitchen makeup air is often passed through a swamp cooler, even in humid environments. Better than nothing, since conventional AC is impractical for that much air volume.

    If Evaporative Cooling (EC) replaced AC in all the cities and towns where it works well, this country would literally never need to build a new power plant. That's because all of our plants are severely underutilized except for a couple weeks in the height of summer when AC units are running full tilt. EC where effective would shave that peak demand, and brownouts would cease until we get enough photovoltaic and wind generation capacity installed. Then we can start decomissioning the coal plants, and voila, EC has solved global warming!
    Yeah, with all that money saved on power, we could build a whole bunch of desalinization plants we would need to supply all that extra water.
    Low Pressure Forever!

    If you know heavy metal, you can work anywhere-Dave Andreson

    Anchors Aweigh my boys, Anchors Aweigh!
    Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!

  7. #27
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    Quote Originally Posted by kevin_in_denver View Post
    Commercial kitchen makeup air is often passed through a swamp cooler, even in humid environments. Better than nothing, since conventional AC is impractical for that much air volume.

    If Evaporative Cooling (EC) replaced AC in all the cities and towns where it works well, this country would literally never need to build a new power plant. That's because all of our plants are severely underutilized except for a couple weeks in the height of summer when AC units are running full tilt. EC where effective would shave that peak demand, and brownouts would cease until we get enough photovoltaic and wind generation capacity installed. Then we can start decomissioning the coal plants, and voila, EC has solved global warming!

    Got news for ya, Tucson Electric did a study a number of years ago and found in Arizona ( you could say its kinda dry here ) a 12 SEER will match the efficiency of an EC.
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  8. #28
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    Quote Originally Posted by kevin_in_denver View Post

    (Note to Garya505: Pollen gets scrubbed from the air that passes thru a cooler. I have seen a little mold on the inside of cooler occasionally, however.)
    Sorry simple not true, the dirtiest duct systems we see have EC's piggy backed on to there A/C system.
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  9. #29
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    2,660
    Post Likes
    Quote Originally Posted by spotts View Post
    I hate Swamp Coolers
    You would, you only do A/C anyway (LOL).

    I have 2 on the place and mostly like the air throughput (remember they are 100% OSA). Plus the Utility bill is a bunch smaller than the neighbor with central A/C by about $40.00/mo.

    I don't know if I would put in A/C even buying it at wholesale.

    It's really nice in the evenings when we can simply use the fan and "Ventilate" the house.

    I disagree about the 80* comment. If you do your homework the measured (DB) discaharge air temp drop should run 25 degree Delta T from OSA DB. I think the RSES SAM manual has a section that makes reference to a 34 Theoretical DeltaT but I can't find it right now. Lat time I checked it costs about 6 cents/hr to operate a EC (Swamp cooler) compared to around 26-30 cents/hr for A/C. If that has changed sigificantly I sure someone will correct me.
    Last edited by Cagey57; 09-03-2009 at 09:23 PM. Reason: Thought of more stuff.
    If sense were so common everyone would have it !
    You cannot protect the Stupid from themselves !
    "Experience is the ability to recognize a mistake Before you make it again!" (Stolen Quote)

  10. #30
    Join Date
    Jul 2009
    Location
    Southern Calif.
    Posts
    110
    Post Likes
    Thread Starter
    I had to shut down my swamp last weekend because of the LA fires. It was just passing through way to much smoke. I have the cheap straw pads and although they wash most of the desert dust and cool pretty good for me, they do not filter smoke. My neighbor has the top of the line MasterCool and she said she does not have a problem.
    I changed my AC filters today with some filters that are supposed to remove smoke smell, but I haven’t noticed much difference. Maybe it takes a while.

  11. #31
    Join Date
    Jul 2009
    Location
    Southern Calif.
    Posts
    110
    Post Likes
    Thread Starter
    I was reading about an all green building in a magazine at work today. They were using a cooling tower to cool water at night then store it for cooling during the day. I didn’t have time to read the whole article, but they said they were able to save 40% on the electric bill.
    I was going to bring home the article to finish reading, but I forgot it.

  12. #32
    Join Date
    Jul 2004
    Posts
    31
    Post Likes
    H.E., I admit it's starry-eyed optimism, but it's an easy back-of-the-envelope calculation. On a hot day, figure maybe 20 million compressors, times what, an average 4kw each..... replaced by a 0.4kw EC unit that only runs at night anyway...etc., etc.. equals X number of 10MW power plants not needed.

    CW, water is a non-destructible resource. If we vaporize some in Nevada, it will fall back to earth over Colorado, and flow downhill back to Nevada.

    It's an awesome cycle, and talk about sustainable!

    Suddenly this thread has become a lot more satisfying. Swamp cooler lovers and haters all coming out and stuff.
    Last edited by kevin_in_denver; 09-04-2009 at 12:07 AM. Reason: It was too snarky

  13. #33
    Join Date
    Jul 2004
    Posts
    31
    Post Likes
    JimJ,

    Thanks for more info. Interesting to hear that EC's are sometimes piggybacked on a conventional ducted AC system. That means, of course, that the ducts are probably 5X too small. I've never heard of it, and it sounds pretty crazy unless the whole thing was engineered and controlled properly.

    Now, the ducts may look kind of dirty, but the air in that house is going to be much cleaner and healthier than a non EC house because of all the fresh air that passes through the ad hoc scrubber:

    ASHRAE Standard 62.1 requires a minimum of 100 cfm of fresh air to ensure acceptable IAQ for an average house. If the average EC is 3500cfm, that's 35 times better air than the ASHRAE minimum inside your house.

    As you probably know from experience, undersized ducts always look dirtier because small dust particles get thrown so hard against the duct wall that they impinge and stick, instead of floating all the way through the duct system back into the house.

    As far as electricity savings, the most important thing is demand reduction. In other words, keeping the compressors off in the hot afternoon is more important for eliminating coal plants than the total energy savings. Consumers are more worried about $ savings, which is usually at least 75%. My savings are higher, because, as I said, I run it only at night and when ambient is under 80*. My unit is really cheap with inefficient pads, and I never see a temperature drop of more than 10*, so I don't want to pump air warmer than 70* into the house when I want to cool it. Yes, theoretically they should work better than that.

    It's true that EC's can't really do the job any more in Tucson and Phoenix. Thirty years ago they worked 95% of the time. It may be due to higher ambient humidity, but also higher average temperatures which are mainly due to the urban heat island effect and possibly global warming. I haven't seen the Tucson energy study, but I believe it. In more suitable climates, the EER rating for EC is usually quoted at around 40. (I'm trying to find the source of that number)

    The 1000 gallons per month I use only cost about $2, or $8 per year for water. I don't have to bleed off, but I completely drain it 1-2 times per month. Not gross or overly saline at all.
    Last edited by kevin_in_denver; 09-04-2009 at 12:05 AM. Reason: addressing the Tucson Electric study also

  14. #34
    Join Date
    Jul 2004
    Posts
    31
    Post Likes
    Johnny B60,

    I sincerely apologize, first I hijacked your thread and then I killed it.

    Here's a positive review of a Coolerado that was just posted at Jetson Green:

    "I recently installed a Coolerado C60 on my house to replace my swamp cooler in Louisville, CO. Instead of having 45 to 65% humidity in the house with the swamp cooler, the relative humidity indoors varies between 25 and 40 percent with the Coolerado. The Coolerado doesn't change the absolute humidity of the air coming into the house, but the relative humidity does increase due to the temperature drop. I prefer the Coolerado over a swamp cooler for several reasons:
    1. The air smells great
    2. Summer "warping" of my kitchen cabinet doors producing closure issues no longer occurs.
    3. The variable speed motor largely runs in the lowest speed which is inaudible.
    4. It is like an air conditioner in that it can actually reach the target temperature you have your thermostat set to; The air coming out of the ducts is quite icy.
    5. Winterization procedure is just closing one valve (the water supply), and opening another (solenoid drain)."

    Careful, Coolerados are pricey. But it appears they have solved all of the typical EC problems.

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •