    1/4" lineset for 1.5-ton XL15i?

    Thanks to the great advice I received in this forum, I purchased a 1.5-ton Trane XL15i AC with XV80 furnace this past spring for my 500 sq. ft. upstairs bonus room. So far, it's been a great system, quietly cooling the room and keeping it much more comfortable than the previous 2-ton Carrier contractor-grade model we had.

    My downstairs unit is a 9 year old 3.5-ton Carrier contractor-grade model that I may replace next year if I can get the tax credit again (I get the credit on the system I bought this year).

    Anyway, while having my Carrier unit serviced this year, the technician noted that they would have used a 3/8" lineset for the new Trane XL15i whereas the contractor that installed the XL15i pulled a new 1/4" lineset. Since it is a 1.5-ton system, I think 1/4" is OK but I'd like to be sure. I assume that bigger would be better but is bigger necessary? The length is under 30 feet.

    Is this enough info to confirm whether the 1/4" lineset for the 1.5-ton XL15i is sized correctly?

    Thank you!

  2. #2
    Join Date
    May 2007
    Location
    DC Metro area
    Posts
    3,225
    4TTX5018A1000A
    Line Size - (in.) O.D. Gas 1/2
    Line Size - (in.) O.D. Liquid 3/8

    I'll let the pros comment on whether it would be acceptable.

  3. #3
    Join Date
    Apr 2009
    Posts
    12
    Thank you, Ryan! I see that in the data sheet now (it's funny how you can find something once you know the answer).

    I would like to know what the pros think about this. Is 1/4" OK or should I insist that they pull new a new 3/8" line?

  4. #4
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,646
    I feel like, if the connections at the unit are 3/8", then that's what should be used.

    Some people will say you only loose a fraction of efficency. Well, if the engineers that designed the unit thought so,they would have downsized it to begin with.Just my opinion.

    Unless the piping is impossible to get to, why wouldn't they have used the correct size? The cost is next to nothing, the first time around. Not the second.

  5. #5
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,161
    According to Trane's piping software, which in the world of Trane equipment is considered the final word in any refrigerant pipe sizing question, a 1/4" liquid line is the recommended size for a 1.5 ton R-410A system, even if it is a crazy long 120' line set with 6 elbows and 20' of vertical rise.

    Trane has always recommended using the smallest diameter liquid line that comes in under the pressure drop limitation for the refrigerant being used, because it makes for a more reliable system that contains less total refrigerant.
    If more government is the answer, then it's a really stupid question.

  6. #6
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    31,559
    Next question: did they use the 1/2" vapor line called for? No, I bet they used 3/4"

  7. #7
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    14,940
    Quote Originally Posted by BaldLoonie View Post
    Next question: did they use the 1/2" vapor line called for? No, I bet they used 3/4"
    John, I bet you remember when the old RUUD/Rheems never had anything but a 1/4" liquid line, ah the good old days when an a/c system could actually freeze you out of your home.
    "The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth".










  8. #8
    Join Date
    Apr 2009
    Posts
    12
    Thank you for confirming this, Mark!

    It does look kinda hokey with a 1/4" refrigerant line running into the 1/2" pipe on the unit, which is pinched shut around, and soldered to, the 1/4" line. I guess they provide 1/2" as a standard on all sizes of XL15i.

  9. #9
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by outbacker View Post
    It does look kinda hokey with a 1/4" refrigerant line running into the 1/2" pipe on the unit
    you got something backwards there

    hopefully, you meant the 1/4 inch line is going into the 3/8 line, if not we got problems



    .

  10. #10
    Join Date
    Apr 2009
    Posts
    12
    I'm sure I'm not explaining accurately or clearly.

    The 1/4" refrigerant line runs about 25' from the furnace in the attic to the XL15i outside. There is a short "stub" of a pipe sticking out of the XL15i that looks like 1/2" (it could be 3/8" but it looks like 2x the 1/4" line). The 1/4" line goes into this larger "stub" pipe and the "stub" pipe is squeezed around, and soldered to, the 1/4" line to make it fit.

    I guess the contractor may have added the larger "stub" pipe as a coupling between the standard refrigerant hookup on the XL15i and the new 1/4" line that he ran.

  11. #11
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,646
    Quote Originally Posted by outbacker View Post
    I'm sure I'm not explaining accurately or clearly.

    The 1/4" refrigerant line runs about 25' from the furnace in the attic to the XL15i outside. There is a short "stub" of a pipe sticking out of the XL15i that looks like 1/2" (it could be 3/8" but it looks like 2x the 1/4" line). The 1/4" line goes into this larger "stub" pipe and the "stub" pipe is squeezed around, and soldered to, the 1/4" line to make it fit.

    I guess the contractor may have added the larger "stub" pipe as a coupling between the standard refrigerant hookup on the XL15i and the new 1/4" line that he ran.
    Pictures would help.

  12. #12
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by outbacker View Post
    I'm sure I'm not explaining accurately or clearly.
    that's right

    no math needed here

    there are 2 stubouts on the unit outside, a big one and a smaller one

    is the 1/4 liquid line "in question" going to the bigger one or the smaller one?


    .

  13. #13
    Join Date
    Apr 2009
    Posts
    12
    Here's what it looks like: