Results 1 to 5 of 5
  1. #1
    Join Date
    Feb 2008
    Location
    Dubai
    Posts
    50

    Confused oil level switch-30GX chiller

    can anyone help to give me a good advice how to replace the oil level switch in 30 gx chillers.is it possible without pumpdown the system?any advice much be appreciated.


    Moideen-Dubai

  2. #2
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,512
    You are going to have to recover it or transfer it , but you cannot pump it down . Are you sure it`s bad ?
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  3. #3
    Join Date
    Mar 2004
    Location
    Windsor ON Canada
    Posts
    391
    Be careful with that switched. I replaced one this week because we had oil at the schraeder on the bottom of the vessel but the switch would not make. Replaced switch, inspected old one and it worked every time by adjusting float up and down by hand. Pretty simple device, cannot understand how it wouldn't work inside oil separator. Perhaps the level switch is not at the same height as the schraeder extension inside the barrel. New switch works properly though.

  4. #4
    Join Date
    Mar 2004
    Location
    Windsor ON Canada
    Posts
    391
    You can get the most oil out of the vessel by closing the valve upstream of the internal oil filter and front seating the service valve upstream of the inline filter. Remove the oil from the service port. When no more oil flows you will have about 2 quarts left in the oil separator. The level switch has an "O" ring which makes the seal so you don't have to worry about oil on the threads. This is also a good time to change both oil filters. You will have to isolate as much refrigerant as you can in the condenser and then reclain all the refrigerant remaining in the evaporator and compressor to get the pressure out of the oil separator so that you can remove the switch. Good luck.

  5. #5
    Join Date
    Sep 2007
    Location
    SF Bay Area
    Posts
    130
    Follow Chiller Man's directions. But here's a tip for the older (mid 90's) chillers: the first 30GXs didn't have O-rings on the oil level sensor fittings and tended to leak there (among other places). POE has solvent characteristics that can dissolve some sealants.
    Carrier came up with a sensor retrofit that required the cutting of an O-ring groove in the existing threaded fitting on the separator. Unless that was done, you probably don't have an O-ring there.
    To ensure a good seal and keep the job cleaner, pick up some Loctite #554 and electrical contact cleaner (non-residue type). Pull a vacuum on the separator, loosen the sensor fitting and spray the contact cleaner into and around the fitting, letting the vacuum draw the cleaner up through the threads to flush out the POE. Loctite the threads on the new sensor and quickly swap out the old with the new. If you're fast, you can swap the fitting before any remaining oil can work it's way down onto the freshly cleaned threads.
    I've cured some chronic leaks on 134a systems this way.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •