Thread: Roof job finally done.. warning I posted a book

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Join Date
    Apr 2006
    Location
    Chicagoland
    Posts
    695
    Post Likes

    Roof job finally done.. warning I posted a book

    We were moving units for the roofer so they could reroof .. at the same time we had to re-route all the line sets, electrical, 24v etc.. 40 year old building, it was a mess. Everything was under 2 feet of tar, and while we were working the roofers were pouring tar all around us. At the beginning we had to be covered up from head to toe; something in the paper they were using being like a chemical burn if left on the skin and exposed to sun.

    This started beginning of June.. then the heat hit, imagine 60 older folks in this 5 story condo on my ass about getting the units hooked back up.
    I had to deal with the Association,Roofer, Management company, and 60 owners!
    At the same time trying to keep up with the roofer redoing the stacks, trying to keep all lines clearly marked as not to confuse them since tracing them would be very hard. It took 2 men 3 hours to redo one stack there were 12! I had to personally braze each connection because the roffer would then cover all teh connections up before we had a chance to test em.
    Hundreths of connections but at the end only two leaks and no mismatched wiring or lines WHEW!!!

    we sold 30 new air and 15 furnaces so that`s probably the only reason it was worth it.
    I must have run up and down those 5 flights and all thru teh building about 100 times!
    At teh beginning people were difficult since we had to go to each unit and turn off power.. they wanted seperate appointments and such what a pain!
    At the end the ball was in my corner .. meaning you want AC you`ll be home at such and such time.
    It was the Associations idea to do this during middle of summer but I took all the slack.
    At one point an elderly gentelman (90+) was taken away by ambulance.. I decided it was in my best interest to offer portable a/cs (for a fee) so noone would die and sue us.

    Anyway I`m so glad its OVER!!!

    Several times the roofers would quit due to heat and we would continue to work.. must have been 120* on that roof!
    My wife bought me a 10x10 pop up.. it saved my life!




    Before:












    after cleaning up the mess:

    Last edited by praha99; 07-17-2009 at 06:46 PM.
    Sorry - yesterday was the deadline for all complaints.
    Quick reply to this message Reply  

  2. #2
    Join Date
    Jul 2009
    Location
    Plant City, Florida
    Posts
    2,198
    Post Likes
    What kind of line is that in the 2nd picture?
    Quick reply to this message Reply  

  3. #3
    Join Date
    Apr 2006
    Location
    Chicagoland
    Posts
    695
    Post Likes
    Thread Starter


    Every disconnect was in this shape.. falling apart completely rusted





    All this was done before we could test for leaks:




    After:







    Sorry - yesterday was the deadline for all complaints.
    Quick reply to this message Reply  

  4. #4
    Join Date
    Jul 2009
    Location
    Plant City, Florida
    Posts
    2,198
    Post Likes
    The condensing units look like they are too close to each other.
    Quick reply to this message Reply  

  5. #5
    Join Date
    Apr 2006
    Location
    Chicagoland
    Posts
    695
    Post Likes
    Thread Starter
    HA I knew someone would say that. Always with the negativity lol I love it!.

    Well Bwalley unless you have some levitating units theres nothing I can do about that , platform were sized for 1970 sized units
    It is what it is, it`ll be fine.
    Sorry - yesterday was the deadline for all complaints.
    Quick reply to this message Reply  

  6. #6
    Join Date
    Jul 2009
    Location
    Plant City, Florida
    Posts
    2,198
    Post Likes
    Quote Originally Posted by praha99 View Post
    HA I knew someone would say that. Always with the negativity lol I love it!.

    Well Bwalley unless you have some levitating units theres nothing I can do about that , platform were sized for 1970 sized units
    It is what it is, it`ll be fine.
    Not being negative, just pointing out a fact.

    You could use a prefabricated aluminum stand, like a R.M Enterprises RDCA-80.

    Attach the legs to the deck, install picth pans around the legs, attach the condensing unit to the stand with 4 2" 16 gage straps.

    I am renovating a building built in 1966 and this is how I am attaching the Condensing units to the roof for the split systems and I have to cut the roof and install curbs for the package units.

    This is rated to 120 MPH wind loads.

    We have to keep 30" between our condensing units.
    Quick reply to this message Reply  

  7. #7
    Join Date
    Apr 2006
    Location
    Chicagoland
    Posts
    695
    Post Likes
    Thread Starter
    I can tell you right now theres no way in hell the roofer or the Association would ever allow me to attach anything like that to the roof.
    Sorry - yesterday was the deadline for all complaints.
    Quick reply to this message Reply  

  8. #8
    Join Date
    Oct 2005
    Location
    Indianapolis, IN
    Posts
    598
    Post Likes

    Roof

    Quote Originally Posted by praha99 View Post
    HA I knew someone would say that. Always with the negativity lol I love it!.

    Well Bwalley unless you have some levitating units theres nothing I can do about that , platform were sized for 1970 sized units
    It is what it is, it`ll be fine.
    They might be close, but it looks to me like everything is servicable.

    Those before pics look like an absolute disaster. The early part of that job sounds like hell on earth to me. I hope you and your crew made some good money because it looks like you guys did a ton a work. In my opinion you did a really nice job, everything looks really clean!!
    Quick reply to this message Reply  

  9. #9
    Join Date
    Jul 2009
    Location
    Plant City, Florida
    Posts
    2,198
    Post Likes
    Quote Originally Posted by steelersfan1 View Post
    They might be close, but it looks to me like everything is servicable.

    Those before pics look like an absolute disaster. The early part of that job sounds like hell on earth to me. I hope you and your crew made some good money because it looks like you guys did a ton a work. In my opinion you did a really nice job, everything looks really clean!!
    I doubt American Standard would agree that they are installed correctly.

    I don't know what kind of mechanical code you have in Indiana, but all of the units would have been red tagged in Tampa.

    I agree they had quite a mess to deal with.
    Quick reply to this message Reply  

  10. #10
    Join Date
    Dec 2004
    Location
    newton,mass.
    Posts
    6,109
    Post Likes
    Quote Originally Posted by praha99 View Post
    HA I knew someone would say that. Always with the negativity lol I love it!.

    Well Bwalley unless you have some levitating units theres nothing I can do about that , platform were sized for 1970 sized units
    It is what it is, it`ll be fine.


    Bwally was asking what I was thinking, your response shows you may be thin skinned. You posted on the wall of pride, you should expect some feed back. So, here comes some feed back ... you are wearing sneakers, that's a big no-no here, you have pipes that apparently do levitate as there is no support for them. The disconnects are mounted on the service panels, some stretched tight, the refrigerant lines are not straight and there are a lot of lazy bends. What is with the metal tape, I see a bunch of guys here do that, to me it looks terrible. This is just me, if I was doing the job I would have wood on hand to enlarge the platforms so I had more room, after all they are re-roofing and could roof a bigger platform no problem. Work under those conditions is tough, so some stuff gets not done the way you would like and that sucks. I have been on similar jobs and know it is frustrating, to much mess, to many guys, not enough time, budget constraints, to hot, to cold, to many boss’s. At the end it is done and they are running OK so all is well.


    .
    "Nothing else can poison our culture, corrupt our society or ruin the character of our people like unearned money or unearned opportunity." -- James R. Cook

    "Fooling around with alternating current is just a waste of time. Nobody will use it, ever." Thomas Edison, 1889.
    Quick reply to this message Reply  

  11. #11
    Join Date
    Nov 2007
    Posts
    388
    Post Likes
    LOL at the metal tape liquid line support!

    IMO, the minimum would have been wire ties.

    How come some units have filter driers and some don't?

    Like others have said....you left it in better shape than you got it.
    Quick reply to this message Reply  

  12. #12
    Join Date
    Jun 2007
    Location
    Here. I'm right here i tell you!
    Posts
    472
    Post Likes
    Quote Originally Posted by bwalley View Post
    The condensing units look like they are too close to each other.
    Not only that I would have supported the linesets and I dont think having J-boxes unsupported in the middle of the sealtight is legal according to NEC Code. Hell of a difference though.
    Quick reply to this message Reply  

  13. #13
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    This was a difficult job. The after pictures look great. While there may be some technical differences regarding required distance between units, you did what you could. If you had more space, I'm sure you would have given them a little more breathing room on two sides of the coil. And I think you're right--should be fine. I'm sure you checked all the pressures out, and I'm sure you've seen worse. This is from a HO's perspective. I'd be happy.

    Was it challenging to repair the 2 leaks after the roofers were finished?
    Quick reply to this message Reply  

  14. #14
    Join Date
    Mar 2004
    Location
    Illinois
    Posts
    6,958
    Post Likes
    Not bad...I just don't care for the metal tape or blue tape....but in a pinch I would use purple tape
    Quick reply to this message Reply  

  15. #15
    Join Date
    Dec 2001
    Posts
    1,365
    Post Likes
    Big improvement. Why pull out discos on a comm job?
    Quick reply to this message Reply  

  16. #16
    Join Date
    Apr 2006
    Location
    Chicagoland
    Posts
    695
    Post Likes
    Thread Starter
    You know looking back at the pics what units here do not have 12" spacing on "both sides"??

    I see maybe one.. second and third row all have more than 12" ..



    there was only one row with all new units, the one pictured. The rest all have plenty of spacing. If there was one old unit in the row I then had plenty of room to space them out.
    as evidenced here:



    Maybe you call this a Commercial job but all these units were individual residential units. I`m not up on OSHA regulations if this is a commercial job.. you got me! The guys shoes is a non issue to me.sorry
    The linesets got supported at a later date, my first concern was getting folks A/C
    I like the silver tape it`s stronger and lasts 10x as long as the alternatives
    Sorry - yesterday was the deadline for all complaints.
    Quick reply to this message Reply  

  17. #17
    Join Date
    Jul 2009
    Location
    Plant City, Florida
    Posts
    2,198
    Post Likes
    Quote Originally Posted by praha99 View Post
    You know looking back at the pics what units here do not have 12" spacing on "both sides"??

    I see maybe one.. second and third row all have more than 12" ..

    http://img.photobucket.com/albums/v4...ndodone003.jpg

    there was only one row with all new units, the one pictured. The rest all have plenty of spacing. If there was one old unit in the row I then had plenty of room to space them out.
    as evidenced here:



    Maybe you call this a Commercial job but all these units were individual residential units. I`m not up on OSHA regulations if this is a commercial job.. you got me! The guys shoes is a non issue to me.sorry
    When placing a unit next to another unit, you need 12" per unit, so a minimum of 24", we always have to have 30" or in some cases 36" of side clearance.

    Why did you mount the disconnects on the service panels?

    Multi family, Multi unit is considered commercial work.

    Even if you only do residential work you should follow OSHA guidelines.

    Seriously you may want to pick up 29 CFR (code of federal regulations) 1926, Construction Industry Regulations.

    OSHA hands out $10,000 fines like they are nothing and in some cases they will hand out $100,000+ fines.
    Quick reply to this message Reply  

  18. #18
    Join Date
    Dec 2003
    Posts
    2,851
    Post Likes
    Quote Originally Posted by bwalley View Post
    When placing a unit next to another unit, you need 12" per unit, so a minimum of 24", we always have to have 30" or in some cases 36" of side clearance.

    Why did you mount the disconnects on the service panels?

    Multi family, Multi unit is considered commercial work.

    Even if you only do residential work you should follow OSHA guidelines.

    Seriously you may want to pick up 29 CFR (code of federal regulations) 1926, Construction Industry Regulations.

    OSHA hands out $10,000 fines like they are nothing and in some cases they will hand out $100,000+ fines.
    BS on the OSHA fines. Ive never heard of anyone being fined more than a few thousand bucks. Maybe they are really tough on tennis shoes.
    Quick reply to this message Reply  

  19. #19
    Join Date
    Jul 2009
    Location
    Plant City, Florida
    Posts
    2,198
    Post Likes
    Quote Originally Posted by bigtime View Post
    BS on the OSHA fines. Ive never heard of anyone being fined more than a few thousand bucks. Maybe they are really tough on tennis shoes.
    Here is a $75,000 fine, it is a trenching violation, not a tennis shoe violation.
    http://www.miamiherald.com/news/flor...y/1145914.html

    This one is $49,544
    http://www.highbeam.com/doc/1G1-148032170.html

    $323,000
    http://safety.blr.com/news.aspx?id=100953

    $71,000
    http://boston.bizjournals.com/boston...1/daily49.html

    http://www.osha.gov/pls/oshaweb/owad...SES&p_id=17615
    Quick reply to this message Reply  

  20. #20
    Join Date
    Apr 2006
    Location
    Chicagoland
    Posts
    695
    Post Likes
    Thread Starter
    Quote Originally Posted by bigtime View Post
    BS on the OSHA fines. Ive never heard of anyone being fined more than a few thousand bucks. Maybe they are really tough on tennis shoes.
    In 1996, Congress passed the Small Business Regulatory Enforcement Fairness Act (SBREFA) in response to concerns expressed by the small business community that federal regulations were too numerous, too complex, and too expensive to implement. The legislation also gives small businesses expanded authority to recover attorney’s fees and costs when a federal agency has been found to have acted excessively in enforcing federal regulations.

    $100,000 fines yeah right..
    Sorry - yesterday was the deadline for all complaints.
    Quick reply to this message Reply  

Closed Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •