Figured it out! I have to create a second binary writeable point and link it to the Auto bit of the INET point I'm trying to put back in Automatic. Yes!
Has anybody successfully set up a Jace for Modbus to INET communication? I am able to get the modbus to read and write to the INET data. However, once the point in INET is placed in manual upon the first write, I can't get it to go back to Automatic using Modbus. Any help would be greatly appreciated!
Thanks!