Bad Suction Accumulator
Has Anyone come acoss a bad suction accumulator? Not sure what can go wrong,Have a small chiller ,Floading back,low low load ,has accumulator,R22,suction 20lb,low temp compresor discus.Want to know if a suction accumulator can go bad?thanks
-
07-16-2009, 06:09 AM #2
I've seen them rust through.
Heard of them clogging up the oil return port.
That's about it.
-
07-16-2009, 06:53 PM #3
x2 filled with oil
-
07-16-2009, 07:35 PM #4
X3
I love the smell of phosgene first thing in the morning:
To apply for professional membership click here
Educational forums are open.
If you would like to submit a link or an article or other related info to the EF. click here
-
07-16-2009, 07:42 PM #5
-
07-16-2009, 08:59 PM #6
I agree with JP on this.
First you should verify that there is in fact a flooded condition...and not just assume flooding just because you see frost. What the suction superheat?
Secondly, if there is a flooded condition here, the accumulator won't cure it. It's only intended to handle intermittent surges of liquid.
Let's hear some numbers.
-
07-16-2009, 09:33 PM #7
I think he needs to read this first than get back with us.

http://hvac-talk.com/vbb/showthread.php?t=158850I love the smell of phosgene first thing in the morning:
To apply for professional membership click here
Educational forums are open.
If you would like to submit a link or an article or other related info to the EF. click here
-
07-16-2009, 09:36 PM #8
x4, I had a unit with the same symptoms a couple of months ago, and it was flooding back, pumping the oil out of the compressor as well, turned out to be the wrong undersized txv. New TXV gave it full load.