    Has Anyone come acoss a bad suction accumulator? Not sure what can go wrong,Have a small chiller ,Floading back,low low load ,has accumulator,R22,suction 20lb,low temp compresor discus.Want to know if a suction accumulator can go bad?thanks
    Sep 2006
    Florida
    x2 filled with oil
    florida
    X3
    I love the smell of phosgene first thing in the morning:
    To apply for professional membership click here
    Educational forums are open.
    If you would like to submit a link or an article or other related info to the EF. click here
    Quote Originally Posted by harley91 View Post
    Why do you suspect the accumulator?
    More details about the problem and we may be able to offer some more detailed analysis to help you find a solution.
    Jul 2000
    Treasure Coast/Florida
    I agree with JP on this.
    First you should verify that there is in fact a flooded condition...and not just assume flooding just because you see frost. What the suction superheat?
    Secondly, if there is a flooded condition here, the accumulator won't cure it. It's only intended to handle intermittent surges of liquid.
    Let's hear some numbers.
    florida
    I think he needs to read this first than get back with us.
    http://hvac-talk.com/vbb/showthread.php?t=158850
    May 2009
    In the Hudson Valley of New York
    x4, I had a unit with the same symptoms a couple of months ago, and it was flooding back, pumping the oil out of the compressor as well, turned out to be the wrong undersized txv. New TXV gave it full load.