Liebert CRAC unit - short cycle problem
I'm haveing problems with my liebert with short cycle alarms. I know the alarm triggers when there are 10 starts in a 60 min period... but neither I or my hvac tech can figure out why it's trying to start so much. Anyone here have that problem? or know how to fix it?
-
07-15-2009, 05:13 PM #2
Professional Member
- Join Date
- May 2009
- Location
- northern kentucky
- Posts
- 137
Is this a new install or existing? Maybe to big (not enough load) or did you change equipment and not producing as much heat.
-
07-15-2009, 08:43 PM #3
New Guest
- Join Date
- Jul 2009
- Posts
- 3
Have your tech check the diff. Settings having them set too close will cause short cycling
-
07-15-2009, 09:56 PM #4
Regular Guest
- Join Date
- Dec 2007
- Posts
- 28
diff good idea, oversized unit with low load will do it to. if unit has recip comp maybe bad valves, leaking solenoid. or you could be just low on gas. real question is what kind of mechanic do you have working on this?
-
07-15-2009, 11:01 PM #5
Spread out the dead bands on both temperature and humidity. If the unit is oversized, spread them out more. Allow for the deadbands in the alarm settings, too.
God Bless the USA
-
07-16-2009, 09:44 AM #6
Regular Guest
- Join Date
- Jul 2009
- Posts
- 4
thanks for the responses.
The units are about 10 yrs old, in a Data Center. The temp settings are set close to maintain a steady temp... and the other lieberts, 2 other crac and 3 ACU units are all set at the same settings and I don't have this problem with the others.
Please don't abreviate, I don't know enough about the equipment to know what a "diff" is.
-
07-16-2009, 07:36 PM #7
Professional Member
- Join Date
- Jan 2009
- Location
- Paradise, NL, Canada
- Posts
- 41
If this computer room has a raised floor you can also try relocating the floor panels that are floor grills as far away from the unit as possible to minimize short circuiting of air.
-
07-17-2009, 04:50 AM #8
Professional Member
- Join Date
- Mar 2005
- Posts
- 53
This is not a site for do it yourselfers. Hire a qualified technician to troubleshoot your problems, It will be cheaper in the longrun. We make a living doing this work, I will never understand the guys on this site so willing to give information out.
-
07-17-2009, 06:30 AM #9
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,550
-
07-17-2009, 06:34 AM #10
-
07-17-2009, 08:46 AM #11
-
07-17-2009, 09:22 AM #12
Regular Guest
- Join Date
- Jul 2009
- Posts
- 4
Wow....
thanks for that... maybe a message should be put on the site for others looking for infomation "Don't bother coming here unless you already know everything" .
I AM paying a certified HVAC professional to come in and work on the equipment. I'm trying to see if anyone else had this problem that may help us determine possible causes, at this time, he cannot find the cause.
-
07-17-2009, 12:14 PM #13
Look for differences in locations of supply and return at the different units.
Check the sensor calibrations. Is the "under floor" more, or less, full of piping and wiring around the short cycling unit? Is there simply less load on this unit due to rack location? Is there house air coming in near the unit?
Parallel units can be a big pain. But the world is full of them. And each room is different.God Bless the USA