How to calculate COP of water cooled chiller plant
How to calculate COP of water cooled chiller plant? What are the fields required?
-
07-14-2009, 08:36 AM #2
Professional Member
- Join Date
- Feb 2006
- Posts
- 217
KW refrigeration div by KW electric input to motor.
You need a Kw meter really. Electric KW= KVA x Pf (power factor)
-
07-14-2009, 11:55 PM #3
Regular Guest
- Join Date
- Apr 2009
- Posts
- 9
thanks. but do I need to include all the motors including cooling tower?
-
07-15-2009, 11:12 AM #4
Professional Member
- Join Date
- Feb 2006
- Posts
- 217
that formula is for chiller COP. If you are doing total plant COP, then you need alll pumps and tower fans. Tower fans are cycling so you would need a KWmeter to measure that. BUT CHILLER cop will vary depending on how much load is on chiller ie. 25% Cop is different from 100% COP.
Not sure what you are really looking for.