    How to calculate COP of water cooled chiller plant

    How to calculate COP of water cooled chiller plant? What are the fields required?

  2. #2
    Join Date
    Feb 2006
    Posts
    224
    KW refrigeration div by KW electric input to motor.
    You need a Kw meter really. Electric KW= KVA x Pf (power factor)

  3. #3
    Join Date
    Apr 2009
    Posts
    9
    thanks. but do I need to include all the motors including cooling tower?

  4. #4
    Join Date
    Feb 2006
    Posts
    224
    that formula is for chiller COP. If you are doing total plant COP, then you need alll pumps and tower fans. Tower fans are cycling so you would need a KWmeter to measure that. BUT CHILLER cop will vary depending on how much load is on chiller ie. 25% Cop is different from 100% COP.
    Not sure what you are really looking for.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  