Thread: Should I even consider an early AC replacement?

  1. #1
    Join Date
    Jul 2008
    Posts
    42
    Post Likes

    Should I even consider an early AC replacement?

    I have a 2000 sq ft house in Dallas with 11 ft ceilings. Built in the mid 1990s and the outdoor condenser is the original York 4 ton 10 SEER unit. Indoor evaporator coil was replaced in early 2000s and is a Lennox 5 ton. We've been here a couple of years without any AC problems (AC cleaning/checkup at purchase said it was ok) but it has never cooled the house down very quickly. On days when it is +100, even with the AC running the inside temperature can still creep up a degree or two. Air handler and ducts are in the unconditioned attic. I have taken every other action I can to reduce the heat coming into the house, including: radiant barrier foil, blinds, window tint, extra attic insulation, airtight light cans, and larger attic vents. Windows are already double pane. Even with all the changes I made to the attic, it still gets up to 130 in the summer. But I don't know of a good space to move the air handler out of there.

    My question is, should I consider upgrading the condenser before it dies a natural death? Or is it a waste to throw it away this soon? I was told when we bought the house that we could buy a new 14 SEER unit that would be compatible with the current evaporator coil. I don't know if this is a good idea or not. Alternately, I can just wait for the condenser to break and then do it. If were going to do an early upgrade, I would wait for the fall/winter (no point in paying summer prices if you don't have to).

    I have not called anyone yet to get an estimate because if it's going to cost $ and only save me $100/year on electricity, I don't want to waste their time. I'm paying $0.11/KWH here and using about 11,000 KWH a year, roughly half of that is due to AC usage.

    I know that I have not provided much detail, but I would appreciate any thoughts you have or other factors to consider. Is this even worth investigating? I don't know anything about HVAC.
    Last edited by beenthere; 07-12-2009 at 03:13 PM. Reason: Removed price

  2. #2
    Join Date
    Aug 2008
    Posts
    462
    Post Likes

    How's the Windows

    We just put in Gorell double panes and its helped (we live in MS) also have you called a pro to check yours to make sure its running the best it can?

    Are you using a restrictive filter?

    I'd at least wait through the summer and get something done off season. We got our new 18 SEER Amana HP in early Feb

  3. #3
    Join Date
    Jul 2009
    Location
    Plant City, Florida
    Posts
    2,198
    Post Likes
    If you do a replacement unit, I would replace both the A/H and the condensing unit at the same time, especially since the A/H is 8 years old.

    Can you relocate the A/H into conditioned space, perhaps in a closet or the end of a hallway?

    Window tint won't do much (no matter what the salesperson will tell you), you would be better off with LOWe double pane windows, but you usually won't get a payback on your windows from an energy savings standpoint.

  4. #4
    Join Date
    Jun 2009
    Location
    Central Texas
    Posts
    81
    Post Likes
    you might consider an attic ventilation fan. they don't use much KW but they move a lot of hot air. be sure to have plenty of soffit vents or it may actually suck air out from the conditioned space. radiant barriers in the attic also are effective.

    before you trash your condenser you might have a pro do a heat load calc on your building to see if your unit is undersized. Sounds like it isn't but you never know. Pretty sure cooling load calculations are not sized for 100+ temps here in TX which means most units correctly sized will start falling behind in cooling performance once temps get above approx 97°F

  5. #5
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    I am betting there is not enough airflow through the evaporator coil.
    It takes a lot of airflow for 4-tons, & humidity shouldn't be a problem Dallas, so I'd be tempted to use at least 425 or even 450-cfm per-ton of cooling, that's 1700 or 1800-cfm.

    The ducts could be picking up heat from the attic, or the Return Air may be drawing heat in from the attic!

    Click on udarrell & figure out what face-velocity is needed through the diffusers to achieve the required CFM & BTUH for each room. - Darrell
    Last edited by udarrell; 07-13-2009 at 08:08 AM. Reason: figure out

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •