    I am replacing a 10 seer 2 and 1/2 ton. R22 Trane heatpump condenser with a 13 seer 2 and 1\2 ton. R22 Goodman condenser. My air handler is a Trane. Will there be any issues due to the evap. coil size?

  2. #2
    Join Date
    Jun 2007
    Location
    The Twilight Zone
    Posts
    2,964
    Quote Originally Posted by Brent Ridley View Post
    I am replacing a 10 seer 2 and 1/2 ton. R22 Trane heatpump condenser with a 13 seer 2 and 1\2 ton. R22 Goodman condenser. My air handler is a Trane. Will there be any issues due to the evap. coil size?
    Bad move. Replace the indoor coil with a certified match with the new condenser.

    If you don't, the outdoor coil will be larger than the indoor coil. This may be OK for a straight a/c, if a TXV is added to the indoor coil, but not for a heat pump.

    The charge will never be right, system SEER may be less than 10, btu output will suffer.

    The Moderator, BeenThere, has a presentation that outlines the issues of putting a new 13 SEER condenser with an older evap coil.

    Take care.