    I am replacing a 10 seer 2 and 1/2 ton. R22 Trane heatpump condenser with a 13 seer 2 and 1\2 ton. R22 Goodman condenser. My air handler is a Trane. Will there be any issues due to the evap. coil size?
    Jun 2007
    The Twilight Zone
    Quote Originally Posted by Brent Ridley View Post
    Bad move. Replace the indoor coil with a certified match with the new condenser.
    If you don't, the outdoor coil will be larger than the indoor coil. This may be OK for a straight a/c, if a TXV is added to the indoor coil, but not for a heat pump.
    The charge will never be right, system SEER may be less than 10, btu output will suffer.
    The Moderator, BeenThere, has a presentation that outlines the issues of putting a new 13 SEER condenser with an older evap coil.