    Ductulator

    Can someone please explain to me why .08 is the magic number for the friction rate?

  2. #2
    Join Date
    Nov 2004
    Location
    NJ
    Posts
    1,332
    Post Likes
    .08 is not the magic number.

    The magic number (friction rate) is your available static pressure times 100 divided by your total equivalent length.
    Ed J

  3. #3
    Join Date
    Jul 2005
    Location
    USA
    Posts
    784
    Post Likes
    There is no magic number
    The Bill of Rights ARTICLE II "The Right of the People to Keep and Bear Arms Shall NOT be Infringed".
    [SIZE="4"]

  4. #4
    Join Date
    Jul 2009
    Location
    gods country maui
    Posts
    16
    Post Likes
    Thread Starter
    Quote Originally Posted by Ed Janowiak View Post
    .08 is not the magic number.

    The magic number (friction rate) is your available static pressure times 100 divided by your total equivalent length.
    would you mind showing me an example? Ya see when I try to enquire about this im always told "just use .08". I say why .08 "cuz thats the magic number" and believe it or not ive been taught that in several classes as well they even pre-marked .08 on our ductulators before they handed them out.

    Im just trying to learn here

  5. #5
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,086
    Post Likes
    This was in the pro section, but I don't see anything in here a DIYer could use. I cut and pasted. This is a great explaination and thank you to coolerinfrederick for posting it.

    coolerinfrederick
    Professional Member Join Date: Apr 2006
    Posts: 402

    friction rating on ur ductulator?

    --------------------------------------------------------------------------------

    people this is not your static press., its the actual friction from 90's transitions etc., here's how to find it, i know it can be next to impossible on certain systems but here ya go:



    Look at the blower performance chart for the selected piece of equipment, AH or furnace.

    Find the static pressure at witch it will deliver the desired airflow.
    Add up the pressure drops of all the air side devices at the desired airflow. Coil, filter, heat strips, registers and grills.

    Subtract the sum of all the pressure drops from the static pressure needed for the blower to deliver the desired airflow.
    This gives you the ASP, Available Static Pressure.

    Next figure up the TEL, Total Equivalent Length, of the duct and fittings from the start of the longest return duct to the end of the longest supply duct.

    Then plug the TEL and ASP into the formula: TEL/(ASP x 100)

    This gives you the friction rate you need to set the ductulator to, be sure you have a ductulator for the type of ductwork you are dealing with.

    After determining the minimum size duct needed to move the required CFM at the calculated friction rate, look at the part of the ductulator that shows the velocity.
    If the velocity is above the recommended FPM for the application, move to the next larger size duct that will get the velocity down to where you need it. Dampers will likely need to be adjusted in any branch ducts that you have to upsize to get the velocity down in.
    Beware of advice given by some guy on the Internet.

  6. #6
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    8,494
    Post Likes
    your Dmanual should explain how to determine friction rate.
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  7. #7
    Join Date
    Nov 2004
    Location
    NJ
    Posts
    1,332
    Post Likes
    Quote Originally Posted by Milk man View Post
    This was in the pro section, but I don't see anything in here a DIYer could use. I cut and pasted. This is a great explaination and thank you to coolerinfrederick for posting it.

    coolerinfrederick
    Professional Member Join Date: Apr 2006
    Posts: 402

    friction rating on ur ductulator?

    --------------------------------------------------------------------------------

    people this is not your static press., its the actual friction from 90's transitions etc., here's how to find it, i know it can be next to impossible on certain systems but here ya go:



    Look at the blower performance chart for the selected piece of equipment, AH or furnace.

    Find the static pressure at witch it will deliver the desired airflow.
    Add up the pressure drops of all the air side devices at the desired airflow. Coil, filter, heat strips, registers and grills.

    Subtract the sum of all the pressure drops from the static pressure needed for the blower to deliver the desired airflow.
    This gives you the ASP, Available Static Pressure.

    Next figure up the TEL, Total Equivalent Length, of the duct and fittings from the start of the longest return duct to the end of the longest supply duct.

    Then plug the TEL and ASP into the formula: TEL/(ASP x 100)

    This gives you the friction rate you need to set the ductulator to, be sure you have a ductulator for the type of ductwork you are dealing with.

    After determining the minimum size duct needed to move the required CFM at the calculated friction rate, look at the part of the ductulator that shows the velocity.
    If the velocity is above the recommended FPM for the application, move to the next larger size duct that will get the velocity down to where you need it. Dampers will likely need to be adjusted in any branch ducts that you have to upsize to get the velocity down in.
    It's really hard to condense how to determine friction rate, the poster above did a nice job of doing it. Only thing is the formula is backwards,
    (ASP x 100) / TEL = FR is correct.
    Ed J

  8. #8
    Join Date
    May 2004
    Posts
    2,622
    Post Likes
    Would it be ok to just use .05 all the time for sizing return duct? I know it may be overkill in some situations, but at least it wouldn't be undersized. I know people who use .06 on all returns.

  9. #9
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Before manual D existed, or about the time it was being developed, I was designing commercial/industrial ducting systems. The standard at that time was SMACNA, which all of today's standards grew from. SMACNA air duct design manuals had different recommended static pressure design points, based on 100' of SP, for various applications.

    For residential applications, .1 sp for supply air and .08 sp for return air was the suggested settings for ductulators (which were expensive to buy back then). You also want to pay attention to the FPM of the systems, again, the SMACNA recommendation for residential was 800 fpm for supply trunk, 500 fpm for supply branch ducts and 400 fpm for return ducting.

    In over 25 years of designing residential systems, I have never had an issue using these recommended settings. Just keep in mind that the ductulators are basing the data on 100' of ducting, from the unit to the termination of the air. If your run is under that length, you have a buffer zone, if your run is over that length, you may want to think about increasing the size of that run accordingly.
    Training is important!
    Practical Training is a must!

  10. #10
    Join Date
    Mar 2005
    Location
    5,000 ft
    Posts
    2,407
    Post Likes

    Fitting selection is as important as FR

    Many folks may get the right FR, but loose it in the fitting selection or the installer makes changes from the original design with no thought of consequences.

    Instead of using wyes, some guys will use triangular or square fiber board transition boxes and there goes the figured FR out the window. Some of those boxes have an EL of 125' compared to a wye of 30'.

  11. #11
    Join Date
    Aug 2007
    Location
    South Texas
    Posts
    373
    Post Likes
    I have always used .1 for supply unless any flex will run longer than I like (usually 12') because a trunk line is not installable then I use .08 for a larger cushion. One thing they need to teach in these duct design classes is "Nothing is Certain".
    We have estimated calculations to get us to range, then sometimes common sense and experience takes over. Surprisingly though, many designs come out way within specs.
    If your using flex on the whole job, I would use .08 for sure.
    I've never had issues with this.

  12. #12
    Join Date
    Sep 2007
    Location
    Round Rock, Tx
    Posts
    86
    Post Likes
    I've always used .06ish for returns, and .08 for supply, makes the system a whole lot quieter too. This has always worked well for me, unless it's a green system that rhymes with dude, then all bets are off.

  13. #13
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    24,816
    Post Likes
    Duct design is not my forte, good cliff notes Milkman!

    I have manual D and have read it, referenced it, used it in tests....and I still hate the damn thing!

  14. #14
    Join Date
    May 2007
    Location
    Dry as a bone Tucson
    Posts
    4,866
    Post Likes
    Quote Originally Posted by spam'n'rice View Post
    Can someone please explain to me why .08 is the magic number for the friction rate?
    The magic number comes in "FPM"

    and requires "DAMPERS"
    "I aint going to spit on 30 years of my life" Monte Walsh


+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •