07-09-2009, 12:36 PM #14
-
07-09-2009, 05:18 PM #15
We suggest after that to isolate the indoor coil and lines by pumping down the system and closing off the outdoor units valves. Then pull the lines and indoor coil to 400 micron vacume and hold. If it doesn't rise then that part of the system is tight and concentrate on the outdoor coil and piping. Don't forget to have them leak check the compressor plug area. They can leak at times also. Good luck.
-
07-09-2009, 05:50 PM #16
Useing a vacuum to help you decide where your leak maybe is a non starter
for me. Dirty vacuum pump oil or instrument not working properly can
mislead you. I would rather use nitogen to find the leak.
Instead of the chance of introducing more air to your closed system.Waddya mean don't thaw out the frig with a knive?
-
07-09-2009, 11:22 PM #17
Regular Guest
- Join Date
- Sep 2006
- Location
- Northern Colorado
- Posts
- 12
Yes, your unit is one that MAY contain the faulty part. Goodman says that some of the service valves contained out of spec o-rings. This results in a leak during very low outdoor temperatures. It doesn't matter what method your contractor uses to check for leaks, they won't find it on the affected valves unless they're checking it when it's very cold outside. There is a kit to remedy the problem (SVCK01), it's easily installed. If your system has been low on R410A only after the winter but does fine through the summer it's likely you have a valve that needs the repair kit.
Benjamin
-
07-10-2009, 09:20 AM #18
I agree with using nitrogen with a refrigerant tracer to pinpoint the leak when needed but many systems are not flat when you arrive. With the price of refrigerant, it makes sense to preserve whats left and use other processes first.
I'm mearly suggesting when the leak is not showing up with bubbles or sniffers, this way you can save time and frustration by trying to determine which component to concentrate on. Dirty pump oil shouldn't even be an issue and miscalibrated instruments would only come into play for those who neglect thier equipment and not practice professionalism in their trade. Number one rule is saftey first, then having the proper tools for the job. Pump oil is cheap. We wouldn't run our cars with filthy oil so why not do the same for the pump to insure good vacumes. Promote best practices for our industry and the young techs coming up.
A large portion of my job is to train and provide technical support for over 900 contractors in 3 states. I have been on job sites with many contractors who have spent years "topping off" systems that they have failed to find leaks on, wasting time and customers money. I find poor practices, neglected instruments and laziness. Taking a systematic, comprehensive approach to leak detection, I am able to locate nearly 100% of these failures. There are times when we've had to pump up coils to over 350 pounds of pressure in order to find finpack leaks most likly from formicary corrosion or tubing seam leaks. Most tubing in condencer coils start out as flat sheets they are then crosshatched for heat pumps and riffled for A/C units. Then the flat sheet is rolled and electronically welded when manufactured. If contaminants are present during this process, weak points can show up and cause leaks. They are very difficult to locate with normal operating pressures. Fromicary corrosion put simply, is a chemical reaction that eats away the copper from the outside inward. Kind of an "ants nest" corrosion and is found industry wide. Some areas are hit harder than others but it's been found nation wide.
-
07-10-2009, 02:35 PM #19
Professional Member
- Join Date
- Jul 2009
- Location
- Alabama
- Posts
- 63
An electronic leak detector should be a must have tool for every service tech. I would also use a nitrogen/refrigerant mix to 300 psig. It sometimes takes time to repair leaks and driers and do proper evacuation procedures. When the call book is overloaded alot of mechanics take the quick route.
-
07-10-2009, 05:46 PM #20
Professional Member*
- Join Date
- Dec 2004
- Location
- newton,mass.
- Posts
- 6,109
"Nothing else can poison our culture, corrupt our society or ruin the character of our people like unearned money or unearned opportunity." -- James R. Cook
"Fooling around with alternating current is just a waste of time. Nobody will use it, ever." Thomas Edison, 1889.
-
07-10-2009, 05:50 PM #21
-
07-10-2009, 10:59 PM #22
Regular Guest
- Join Date
- Mar 2006
- Posts
- 19
Sounds Like I have the Same Problem
I called Goodman today and they gave me the general consumer people. They will only let contractors speak to technical support. I asked them if the service bulletin applied to my condenser, she came back with a no, but then again, she had no clue what I was talking about. The contractor came back today and charged the suction side with nitrogen to more than 300psi. He said he does this at his job to find leaks and you can usually find them with bubbles or hear the hissing sound. he checked every component and heard nothing. He even took apart the compressor. I am beginning to think he might be right because I only lose refrigerent over the winter. This winder we had a week of temps at 4 deg (F). Maybe that is why I lost all my r410a. I am going to have him call goodman. Is it hard to replace part in service kit? I love this forum---you guys have always inspired me and I like to take a second to thank you.
-
07-11-2009, 12:04 AM #23
Professional Member
- Join Date
- Oct 2007
- Location
- BC
- Posts
- 312
-
07-11-2009, 12:53 AM #24
Regular Guest
- Join Date
- Mar 2006
- Posts
- 19
the valvues are the high and low side service ports where you hook up the hoses. Two years ago he suspected that it might be that but no leak detecked by bubbles etc.
-
04-20-2010, 05:49 PM #25
New Guest
- Join Date
- Apr 2010
- Posts
- 1
NEW CONTRACTOR!!!!!!!
I KNOW YOU SAID YOU DONT WANT TO CHANGE CONTRACTORS BUT IF YOUR GUY FRANKINSTINED A SYSTEM TOGATHER LIKE THAT HE IS THE LAST PERSON YOU NEED WORKING ON IT AND THEN HE TELLS YOU HE HAS TO GO GET A ELECTRONIC LEAK DETECTOR SOUNDS LIKE JOHNNY JACK LEG WORKING OUT OF HIS MOTHERS BASEMENT. THE GOOD THING ABOUT THIS SITUATION IS YOU GOT A VERY GOOD FURNACE BUT COMPLETE PIECE FOR A AIR CONDITIONER I WOULD FIRE YOUR CONTRACTOR ASAP GET A REAL HVAC MAN AND GET THE PROBLEM FIXED
-
04-20-2010, 06:21 PM #26
Professional Member*
- Join Date
- Dec 2004
- Location
- newton,mass.
- Posts
- 6,109
Hey xraymarc,
This poster is writing from his mom's basement, he has to be, first post and no profile and he's judging your contractor. Your contractor could be just fine or not, we do not know. You seem OK at the moment with him so I think you should hang in there a while with him ... he did come back after all. There have been some good post here to help you ... listen to them.
Maybe this poster is an imposter and knows you or your contractor … just saying.