    Some guy's just don't read the GIANT RED TAG!!! they put on the suction valve I guess. Why would it hurt the compressor with nitrogen in the system??? I know it does not work with it in there but why would it hurt the mompressor?

  2. #41
    Join Date
    Dec 2007
    Location
    Midwest
    Posts
    638
    300 head no subcooling at sight glass, 70 suction hardly any delta at indoor coil

    One of two things, it is either not R22 by itself in it or you have a major restriction before the sight glass.

    Just check your LL temp at outlet of condenser, if you don't have subcooling there you have non condensible in the system or a plugged condenser,

    You're welcome,

  3. #42
    Join Date
    Jun 2008
    Location
    NW Florida
    Posts
    713
    Quote Originally Posted by douknowq View Post
    Some guy's just don't read the GIANT RED TAG!!! they put on the suction valve I guess. Why would it hurt the compressor with nitrogen in the system??? I know it does not work with it in there but why would it hurt the mompressor?
    Remember, that compressors rely on cool gas to cool them. With the nitrogen in it there was very little cooling going on since nitrogen does not absorb any heat in its gas state. Hence compressors would eventually over heat. If that happens to often it will eventually cook the windings.

Page 4 of 4 FirstFirst 1234

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event