Results 1 to 8 of 8
    san antonio
    Confused Trane TWA048C300A2 contactor not engaging all the way
    Heat Pump Trane TWA048C300A2
    Air Handler Trane TWE048C140B3
    When calling for cooling, I am reading 24-25 volts at condenser contactor. That should be enough to energize the contacts competely. I saw that the original contactor was pitted, so I replaced it with a new one (right one) and I am still getting almost a low voltage signal that barely engages contacts half way. I can sometimes press the contactor manually and it will stay in. Possibly a bad transformer? Anyone else got any other suggestions?
    Quote Originally Posted by sanantoniotech View Post
    Just cuz it's a new contactor, doesn't mean it's gotta work.
    You've got the posts, apply for pro, and get more detailed answers.
    san antonio
    PROBLEM SOLVED!!!!!!!
    Wrangler...you were right, it might be new, 'but was it the right contactor.' I went and double checked to find out that a 110-120 volt coil contactor was put in a 24volt contactor box. Guess I need to read directly off the contactor from now on...Thanks everyone!
    Sometimes ya just gotta be smarter than the machine.
    From this day on, you'll always check the coil voltage, won't ya?
    Jun 2008
    Cincinnati, Ohio
    Sounds like PHB's rule (I named it myself.......)
    "You only have to be 2% smarter than whatever it is you're working on"
    Still, apply for pro membership!
    Or we'll erase your memory, or this thread.
    Or both.