    I have the following Trane equipment installed:

    Furnace: 60,000BTU Trane XV95

    Compressor: 2 Ton Trane xl15i 4TTX5024A

    Coil: 4TXCB025BC3

    I do have 100amp service

    When the compressor first kicks on the lights noticeably dim for a split second. After that they are fine. I remember reading that Trane offered a free Hard Start kit. Is there one available for my unit? Thanks

    Teddy

  2. #2
    Join Date
    Jul 2009
    Location
    Plant City, Florida
    Posts
    2,198
    Quote Originally Posted by teddyc27 View Post
    I have the following Trane equipment installed:

    Furnace: 60,000BTU Trane XV95

    Compressor: 2 Ton Trane xl15i 4TTX5024A

    Coil: 4TXCB025BC3

    I do have 100amp service

    When the compressor first kicks on the lights noticeably dim for a split second. After that they are fine. I remember reading that Trane offered a free Hard Start kit. Is there one available for my unit? Thanks

    Teddy
    Have a qualified Licensed electrician check for a loose connection, but it is most likely to what is called inrush, where the starting amperage is up to 5 times the run amperage, and with only a 100 amp service, that is what would cause it.

    If you need a hard start talk to your Licensed A/C contractor about it.

  3. #3
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    That 2 ton XL15i has a factory installed start kit in it.
    The start kit doesn't reduce the peak amperage on start-up, it just reduces the length of time it is at the peak amperage.

    Is the dimming just a brief flicker, or does it dim the lights for a couple of seconds when it starts?
    If more government is the answer, then it's a really stupid question.

  4. #4
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,371
    I too sometimes notice a brief dim flicker upon startup (<1 second), but never thought much about it. Curious to see what the pros have to say about this one.

  5. #5
    Join Date
    Jul 2009
    Location
    Plant City, Florida
    Posts
    2,198
    Quote Originally Posted by RyanHughes View Post
    I too sometimes notice a brief dim flicker upon startup (<1 second), but never thought much about it. Curious to see what the pros have to say about this one.
    I already explained what the issue is.

    a 100 amp service is on the small side, with a compressor that pulls 12 FLA it can pull 60 amps Briefly at start up, maybe slightly more.

  6. #6
    Join Date
    Jan 2008
    Posts
    2,118
    Check to see if the A/C breaker is installed nearest to the main breaker. If not, call an electrician.
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler

  7. #7
    Join Date
    Mar 2008
    Posts
    87
    Thanks guys. Lots of good info here.

    1. I had an electrician out to look at my panel about 1 month before the AC install. He said everything looked good. I do notice a smaller flicker also when the dryer, fridge and dehumidifier first turn on.

    2. The dimming from the AC is a brief flicker. Its not horrible, but if there was an easy fix I would get it taken care of.

    3. I have attached a document I found online that shows the "Start Components" (I would assume the same as a hard start kit) are factory installed on the 2 ton. Strange how some of the other sizes in the document do not have that. I think the confusion came from, the R22 version of the XL15i start kit was optional. I found an old document that showed this. I guess the R-410a models are different.

    4. On my breaker there is a left and right side. My AC is the highest breaker on the right side. Is that nearest to the main breaker?

    Thanks

    Teddy
    Attached Images Attached Images

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event