    Have a weird one guys need your help!!

    Customer needed a new condensor and wanted a Ducan! I tryed talking him out of it but he insisted so thats what we put in! 2 ton,13 seer, R22...

    OK heres what its doing! we got 65 psi on the low side and 200 psi on the high.

    we have around a 20 degree temp drop between return air and supply air.

    But the system has been running for three hours and temp has only dropped two degrees. its around 80 degrees outside.

    the suction line is not sweeting and the condisate has only dripped two litttle drops in the time its been running.

    we have a high superheat of 26...and our subcooling is 12.....

    but what we cant figure out is its cooling the air but something is off...the return air temp was 78 and it was blowing aroung 59 degrees?

    dose any one have any suggestions???

  2. #2
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,831
    Yes, but can't discuss this in the open forums. Sorry.

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,808
    Sorry, this is not a DIY site. So we are not allowed to give out advise of this nature.

    Since answering your question in the open Residential Forums would be posting instruction for DIYers that may read this post later.

    If your in the trade, get your post count up to 15, and apply for Pro Membership.
    Then use this link Apply for Pro Membership

    Once accepted, you have access to the pro tech forums. Where you can ask and get answers to technical questions.

    Plus, you also have access to the Pro Educational Forums.

    All of it is free.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,808
    Just curious. Did you happen to also install a new indoor coil.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    ok thanks i am in the field..how do i get my post count up to 15..do I have to post 15 topics in order to apply for the pro membership?

  6. #6
    No i did not replace the coil..i did however change the piston in the metering devise!

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,808
    15 post.
    They can all be in the same thread.

    Nice if they aren't though.

    You might want to go to the general forum, and introduce yourself.
    Its a nice way of meeting teh rest of us. Even teh vranky ones like me. LOL
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,808
    Quote Originally Posted by hybridhvac View Post
    No i did not replace the coil..i did however change the piston in the metering devise!
    Well, you got one problem right there.

    You now have a 2 ton condenser, probably only ale to do 1.5 to 1.7 tons of work.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    ok! I will def intro myself in the forums..and i dont want to keep asking questions in here because you just told me we cant disscuss this in here but the condensor i took out was also a 2 ton...

  10. #10
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,831
    Quote Originally Posted by hybridhvac View Post
    ok! I will def intro myself in the forums..and i dont want to keep asking questions in here because you just told me we cant disscuss this in here but the condensor i took out was also a 2 ton...
    Bet ya it wasn't a 13 seer though.

  11. #11
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,808
    As above. it probably was a 10 or 8 SEER.

    Read this attachment.
    Attached Images Attached Images
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #12
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,831
    Quote Originally Posted by hybridhvac View Post
    ok! I will def intro myself in the forums..and i dont want to keep asking questions in here because you just told me we cant disscuss this in here but the condensor i took out was also a 2 ton...
    Well, now you have five posts, almost half way there.

  13. #13
    Join Date
    Dec 2007
    Location
    Ohio
    Posts
    2,875
    This really isn't a weird one.....LOL


    Get your post count up and apply.....then we can explain why.....


    Beenthere is definitely on to something here.....
    I need a new signature.....

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event