  1. #14
    Join Date
    Sep 2002
    Location
    Northeast Ohio
    Posts
    4,842
    Your installer just needs to spend a little more time confirming charge and air flow. TXV means he HAS to charge using super heat / sub cool methods. As far as sweating, only an indication that you are too hot.
    A good HVAC tech knows how, an educated HVAC tech knows why!

    DEM


  2. #15
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    4,977
    The indoor split is contingent on the humidity level.
    If the indoor humidity is high, a 16-F split would be okay.

    The normal blower position blows air through the coil, & therefore the only increase in its percentage of normal air pass-through (by-pass) would be due to the increase in velocity & CFM through the indoor coil - with blower door-panel removed.

    If the blower is drawing air through the coil, with blower door removed, it could be a near total by-pass of the indoor coil. The TXV would shut the liquid flow way down helping to protect the compressor; a fixed orifice metering device would in a short time, be a major liquid slugging threat to the compressor.

    Check duct system for air leaks & check for required airflow, correct CFM if needed, then charge using Subcooling & verify TXV's specified Superheat setting.
    Last edited by udarrell; 07-07-2009 at 12:00 PM. Reason: wording change

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event