    Please help me help my tech

    First, a timeline:
    April 30, 2009: Tech replaces evap. coil because pan has rusted through
    June 14, 2009: A/C stops cooling altogether
    June 15, 2009: Tech finds it frozen up and 6 lbs (out of ~8 lbs) low on refrigerant. Replaces refrigerant. Can't find a leak
    June 16, 2009: Tech comes back because of inadequate cooling. Finds obstruction in filter drier and replaces it, and cleans condenser unit.
    June 19, 2009: Tech comes back because of inadequate cooling. No problems found. Adds some refrigerant, but says it didn't really need it.

    The A/C hasn't been working correctly since it initially froze up, though it is blowing cold air. It functions fine from about midnight to 10AM and has a return/supply differential of 20 deg F (78-58). Starting at around 10AM it struggles to maintain 80 deg F and the house slowly heats up to 85-87 deg F, peaking in the late afternoon. The return/supply differential shrinks to ~13-14 deg F. It takes until midnight to cool back down to 80. It runs constantly from 10ish until midnight.

    It is an older system (16 years) and has been trouble free until the leaking pan issue. I would've had the whole thing replaced, but I am moving within a year and it had been performing wonderfully besides the leak.

    The tech is coming back tomorrow to take a look again and I want to be able to ask intelligent questions when he does. Ignoring the potential of having a leak, what could cause this type of performance issue?

    My guesses so far:

    1) Compressor problems (he said he checked it and it showed signs of age, but it was functioning OK.)
    2) Large cold air leak in attic (I looked and didn't find anything).
    3) Blower problem
    4) Expansion valve problem
    5) Improper charging procedure
    6) Improperly sized replacement evap. coil
    7) ??

    Do all of these make sense for the issues I am having? Can you add any more?

    I appreciate any help I get.
    Thanks,
    Jeff

  2. #2
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,847
    Time to call in the pros. This guy is guessing at things.

  3. #3
    Join Date
    Jul 2002
    Location
    Zelienople, Pa
    Posts
    2,965
    I would've had the whole thing replaced, but I am moving within a year and it had been performing wonderfully besides the leak.

    So you're going to leave the new owner with a cobbed up mess...

    Nice guy.
    How tall are you Private???!!!!

  4. #4
    Join Date
    Mar 2005
    Location
    Suppy NC
    Posts
    4,513
    from the ammout of times refrigerant is added sounds like a leak somewhere and needs to be fixed.

    if the system was evacuated and charged properly then it should not never need refrigerant added again unless it has a leak

  5. #5
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,847
    Quote Originally Posted by Gunnery Sergeant Hartman View Post
    I would've had the whole thing replaced, but I am moving within a year and it had been performing wonderfully besides the leak.

    So you're going to leave the new owner with a cobbed up mess...

    Nice guy.
    That was my first thought too.

  6. #6
    Join Date
    Jun 2009
    Location
    NAPLES,FL
    Posts
    38

    Cool

    BINGO! I found your problem..............your tech.

  7. #7
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    2,990
    easy!! Purchase a new HVAC system (not from this Co.), the new owner will appreciate this! (it deff wont hurt selling your home)

    2. Get a new tech!

    Those are your options.

    You cant be guessing like your tech... Where did you come up with that list anyway?
    Gotta have the right tool for the job!

    Where is all the stuff MADE IN THE USA?

    "Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."

  8. #8
    Join Date
    Jul 2006
    Location
    NW burbs of Detroit
    Posts
    6,058
    Quote Originally Posted by Gunnery Sergeant Hartman View Post
    I would've had the whole thing replaced, but I am moving within a year and it had been performing wonderfully besides the leak.

    So you're going to leave the new owner with a cobbed up mess...

    Nice guy.
    ROTFLMAO!!!!!!!!!!!!

  9. #9
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    4,904

    Return Air drawing hot air from the attic or garage area?

    Quote Originally Posted by MEENag View Post
    First, a timeline:
    April 30, 2009: Tech replaces evap. coil because pan has rusted through
    June 14, 2009: A/C stops cooling altogether
    June 15, 2009: Tech finds it frozen up and 6 lbs (out of ~8 lbs) low on refrigerant. Replaces refrigerant. Can't find a leak
    June 16, 2009: Tech comes back because of inadequate cooling. Finds obstruction in filter drier and replaces it, and cleans condenser unit.
    June 19, 2009: Tech comes back because of inadequate cooling. No problems found. Adds some refrigerant, but says it didn't really need it.

    The A/C hasn't been working correctly since it initially froze up, though it is blowing cold air. It functions fine from about midnight to 10AM and has a return/supply differential of 20 deg F (78-58). Starting at around 10AM it struggles to maintain 80 deg F and the house slowly heats up to 85-87 deg F, peaking in the late afternoon. The return/supply differential shrinks to ~13-14 deg F. It takes until midnight to cool back down to 80. It runs constantly from 10ish until midnight.

    It is an older system (16 years) and has been trouble free until the leaking pan issue. I would've had the whole thing replaced, but I am moving within a year and it had been performing wonderfully besides the leak.

    The tech is coming back tomorrow to take a look again and I want to be able to ask intelligent questions when he does. Ignoring the potential of having a leak, what could cause this type of performance issue?

    My guesses so far:

    1) Compressor problems (he said he checked it and it showed signs of age, but it was functioning OK.)
    2) Large cold air leak in attic (I looked and didn't find anything).
    3) Blower problem
    4) Expansion valve problem
    5) Improper charging procedure
    6) Improperly sized replacement evap. coil
    7) ??

    Do all of these make sense for the issues I am having? Can you add any more?

    I appreciate any help I get.
    Thanks,
    Jeff
    Perhaps, none of the above...

    It sounds like the Return Air is drawing hot air from the attic or garage areas.

    When those areas are not so hot it cools better & has close to a normal indoor SA/RA temp-split.

    When those areas get hot, bingo it no longer can handle that extra hot-air heatload.

    First, check the Condensing Temperature (CT) verses the outdoor Ambient (OAT). The CT spread will increase during the hot part of the afternoon & into the evening.

    First, check for temp changes at Return Registers, then just before air enters the blower. Much temp increase during those hot periods? Depends on how the Return Air is ducted as to where you're most likely to find those air leaks. If chamber under the furnace, air could be coming down unsealed walls into the chamber.

    Correct any Return Air problems. -Darrell
    Last edited by udarrell; 06-29-2009 at 11:58 PM. Reason: Re-worded

  10. #10
    Join Date
    Jun 2009
    Posts
    11
    Quote Originally Posted by Gunnery Sergeant Hartman View Post
    I would've had the whole thing replaced, but I am moving within a year and it had been performing wonderfully besides the leak.

    So you're going to leave the new owner with a cobbed up mess...

    Nice guy.
    When I said "besides the leak", I meant the rusted evaporator coil pan that I had replaced, not the potential refrigerant leak that hadn't happened yet.

    When I decided to replace just the evaporator coil because of the rusted pan and not get a whole new system, my thinking was that my system had performed without flaw for 16 years and that it might well last another 4-5+ years. It wasn't about the money, well partially, but it was more about not wanting to trash a perfectly good system. Whoever buys the house will know the age of the system and will take that into account when making an offer and I won't have a problem making concessions for it. Thanks for making a judgement on my character though.

    Pascone10,
    Where did I come up with that list? I made it up and came here and asked if any of them made sense and if anyone had other ideas. Clearly I'm no HVAC pro.

    Please shoot down any of my guesses that don't make sense.


    If I thought this process would've been any more than a quick evap. coil swap, then I would've had the system replaced.


    The tech is a nice guy and was recommended by several people. He charged me a small amount for his first visit after the evaporator coil replacement and didn't charge anything for the next two visits. He's the owner of a two truck independent business and has probably lost money because of accepting my job. I figure I'll give him another chance tomorrow and then call in someone else if he can't figure it out.

    Darrell,
    Excellent suggestion. That's the kind of information I was looking for. Thanks.

  11. #11
    Join Date
    Dec 2002
    Location
    Toledo, Ohio, United States
    Posts
    12,910
    Twilli says HVAC guys are hard on H/O's. Cause some of them used to be H/O's themselves
    No Heat No Cool You need Action Fast

  12. #12
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    4,904

    Yes, I'm a s

    It appears everyone is avoiding a response to my post explaining why all the symptomatic experience data points to hot air sources entering the Return Air.

    Because of when the indoor split is reduced, e.g., when the attic or garage would be hot, it is an easy diagnosis. The indoor temp-split is mainly dependent on indoor Return Air temp & humidity levels.

    Additionally what is the humidity levels in your attic or garage.

    I have seen & solved this problem many times during my many decades as a Tech & Contractor. Smaller Return Air leaks are usually overlooked leading to costly inefficient performance.

    It is possible you might learn a little HVAC by going to my Internet pages, for this month of June alone hits appear to be going over 80,000, & the HVAC pages lead all other pages by a wide margin for number of hits.

    Do you want to solve the problem or just talk about it?
    If you don't want to respond to my analysis, perhaps I should quit trying to help anyone solve their air conditioning problems.

    Why should I spend any time & effort in an attempt to help anyone solve their problem on this forum, when I'm ignored & when there is no feed-back?

    I guess I'm a spoiled child, I want a two-way communication, or it's so-long it's been good to know you.

    You might spend a fortune on new ultra high efficiency equipment & end up with hot-air, pardon the pun. - Darrell
    Last edited by udarrell; 06-30-2009 at 07:54 AM. Reason: Sorry, I hit Enter instead of Shift Key, so title, post not finished

  13. #13
    Join Date
    Jun 2009
    Location
    Somewhere in the airconditioned world!
    Posts
    20
    Loss of refrigerant and the tech found no leak

    Quote Originally Posted by francosair View Post
    BINGO! I found your problem..............your tech.
    Maybe the tech has a leak

Page 1 of 5 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event