06-18-2009, 11:24 PM #1
Regular Guest
- Join Date
- Jun 2009
- Posts
- 7
Contactor not pulling in
I've been working on a Carrier RTU Model 50hjq014. First time found the contactor not pulling even though had correct voltage at contactor. Just touched contactor and it pulls in. I replaced contactor and it worked fine for about a month. Called back out same problem. Checked for loose wiring, bad ground (contactor 120v coil), pressure switches. Couldn't find anything wrong, but went ahead and tried another contactor. Works for about a month then same problem happens. Tried even replacing current sensing switches. And it happened again. Any suggestions would be appreciated, maybe Im missing some kind of stat or switch that is on the unit.
-
06-18-2009, 11:50 PM #2
Regular Guest
- Join Date
- Jun 2009
- Location
- Ancaster,Ontario
- Posts
- 27
does this unit have an economizer?
-
06-18-2009, 11:53 PM #3
Regular Guest
- Join Date
- Jun 2009
- Posts
- 7
No this unit does not have an economizer.
-
06-18-2009, 11:54 PM #4
Regular Guest
- Join Date
- Jun 2009
- Location
- Ancaster,Ontario
- Posts
- 27
how did the contacts look on the replaced contactors?
-
06-19-2009, 08:54 AM #5
Regular Guest
- Join Date
- Jun 2009
- Posts
- 7
contacts looked good. no pitting or burning. looked pretty much new.
-
06-19-2009, 09:12 AM #6
-
06-19-2009, 09:17 AM #7
Regular Guest
- Join Date
- Jun 2009
- Location
- massachusetts
- Posts
- 22
Maybe your contactor should be 240v, did you ever check original that you took out
-
06-19-2009, 10:15 AM #8
Professional Member
- Join Date
- Sep 2008
- Location
- Da' Mitten
- Posts
- 71
I've seen something similar with units that have a delay on make timer on them to prevent short cycling when the stat is being fiddled with..
The timer works properly most of the time, but every so often it passes correct voltage but not enough current to pull in the coil on the contactor. When this happens you see correct voltage and the contactor still does nothing.
Does the replaced contactor work properly when 120 is applied to the coil after replacement? If so it would indicate the problem is not the contactor but the board or the stat.
-
06-19-2009, 08:23 PM #9
Regular Guest
- Join Date
- Dec 2007
- Posts
- 28
IS YOUR CONTACTER CHATTERING? CHECK THE VA RATING ON YOUR TRANSFORMER SEE WHAT YOUR PULLING. IF YOUR USING WHAT EVER CONTACTOR YOU HAVE ON YOUR TRUCK IF YOU GO TO BIG YOUR TRANSFORMER MIGHT NOT BE ABLE TO PULL IT IN. TRY BUMPING UP THE SIZE OF YOUR TRANSFORMER.
-
06-19-2009, 10:10 PM #10
Regular Guest
- Join Date
- Jun 2009
- Posts
- 7
-
06-19-2009, 10:12 PM #11
Regular Guest
- Join Date
- Jun 2009
- Posts
- 7
-
06-20-2009, 10:49 AM #12
Professional Member
- Join Date
- Jan 2005
- Posts
- 587
-
06-20-2009, 11:43 AM #13
Professional Member*
- Join Date
- Mar 2009
- Location
- Several Miles from Sane
- Posts
- 1,409
referjman, turn off the capslock, it's like you're yelling !
Check the inrush and holding VA requiremenrs for the contactor, had 1 recently that worked fine when I was there but 4 hours later it wouldn't pull in. The holding current was 22VA but the inrush was 75VA. Transformer was, you guessed it 75VA. That was on 24VAC circuit but I have also seen it happen on 120 control circuits. If you can find out what Original Make/Model was, that may solve your problem. Also check to see if you have a pilot relay that controls the contactor, that deserves a look also.If sense were so common everyone would have it !
All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!